Wiring induction hob

Comments

  • Registered Users, Registered Users 2 Posts: 1,854 ✭✭✭Deagol


    It says it needs 4600watts connection rating. 4.6kW is maximum ~22.5amps. 6mm2 cable is specified for 32amps.

    Can't see any reason you can't use it. I wouldn't think you can buy a domestic hob that exceeds the standard 32amp MCB / 6mm2 used in Ireland.

    Maybe a sparky will correct me though!



  • Registered Users, Registered Users 2 Posts: 45 snx92


    Thanks very helpful! Any electricians that could confirm please ?



  • Registered Users, Registered Users 2 Posts: 4,922 ✭✭✭meercat


    it is ok for a standard 6mm 32amp supply


    the issue could be if you also have an oven on the same circuit (especially a double oven)


    diversity does apply as it’s unlikely (but not impossible)that you would have all the rings on at the same time along with the ovens working



  • Registered Users, Registered Users 2 Posts: 45 snx92


    Thanks a million the oven is on a separate circuit.



  • Registered Users, Registered Users 2 Posts: 4,922 ✭✭✭meercat




  • Advertisement
  • Registered Users, Registered Users 2 Posts: 45 snx92


    Thanks a million you're very good much appreciated



  • Registered Users, Registered Users 2 Posts: 37 Paul.kavanagh


    Diversity is the main thing to factor in when it comes to high load circuits. Especially when it comes to cooking lines.