Socket for Oven

  • 07-01-2025 08:23AM
    #1
    Registered Users, Registered Users 2 Posts: 40


    Could anybody with experience or knowledge advise on below? Thanks in advance

    • Oven & Hob on same 32amp circuit. Designer has applied diversity. Oven has come with a 13amp plug & a single socket has been added adjacent the cooker connection unit behind the oven/under the hob. The 32amp circuit is not RCD protected. Due to the socket now added to the circuit is there a requirement to protect the 32amp circuit with RCD?


Comments

  • Registered Users, Registered Users 2 Posts: 40 LarryBarry


    anybody 😂



  • Registered Users, Registered Users 2 Posts: 720 ✭✭✭Hoagy


    Sockets used as isolation for fixed appliances do not require RCD protection provided measures are taken to prevent their use for general purposes.A warning notice should be fitted adjacent to the socket.

    So if the socket is inaccessible an RCD is not required.



  • Registered Users, Registered Users 2 Posts: 4,908 ✭✭✭meercat


    can you back this up and point the relevant regulation out. Cheers.



  • Registered Users, Registered Users 2 Posts: 720 ✭✭✭Hoagy


    Yes, it's 554.4.2 page 336



  • Registered Users, Registered Users 2 Posts: 40 LarryBarry


    Hi Thanks for that



  • Advertisement
  • Registered Users, Registered Users 2 Posts: 4,908 ✭✭✭meercat


    thanks for that Hoagy

    I’m just playing devils advocate here now for discussion purposes


    would an integrated fridge, microwave ,dishwasher,washing machine,kitchen extractor fan etc be considered under the same category as per your previous post


    “Sockets used as isolation for fixed appliances do not require RCD protection provided measures are taken to prevent their use for general purposes.A warning notice should be fitted adjacent to the socket.

    So if the socket is inaccessible an RCD is not required.”



  • Registered Users, Registered Users 2 Posts: 720 ✭✭✭Hoagy


    But the rule only concerns fixed appliances rather than integrated.

    My post was referring to this particular oven socket in the OP being inaccessible.

    I'm involved in new builds and this situation arises quite often. The alternative is to remove the plug top and connect the oven directly through a joint box.



  • Moderators, Home & Garden Moderators Posts: 6,509 Mod ✭✭✭✭Wearb


    The alternative is to remove the plug top and connect the oven directly through a joint box.

    In such an instance, I suppose it would be necessary to provide a fused spur, to maintain the 13A rating of the provided cable?



  • Registered Users, Registered Users 2 Posts: 720 ✭✭✭Hoagy


    Yes it would.



  • Registered Users, Registered Users 2 Posts: 4,908 ✭✭✭meercat


    thanks Hoagy

    And what determines a fixed appliance

    Would an integrated appliance (microwave,dishwasher etc)that has to be unscrewed be any different from an oven that also has to be unscrewed.

    You say that if a socket is inaccessible it doesn’t need rcd protection



  • Advertisement
  • Registered Users, Registered Users 2 Posts: 720 ✭✭✭Hoagy


    No, I said that the socket described in the OP, in the particular location behind the oven and below the hob, would be considered sufficiently inaccessible to satisfy the quoted rule. I would go no further than that.

    Whether the rule could be applied in other cases would be a matter for the REC involved.



  • Registered Users, Registered Users 2 Posts: 4,908 ✭✭✭meercat


    sorry hoagy about delay getting back to you on this. I see you quoted the relevant regulation thanks but I think you have misinterpreted it.

    “554.4.2 circuits supplying socket outlets provided for the isolation of fixed equipment in accordance with 537.2 need not be protected by RCDs provided effective measures have been taken to prevent their use for general purposes.
    Note :
    such equipment includes motors and fluorescent lamps

    A suitable warning notice shall be provided at location”

    The important part of this paragraph is that it's for isolation of fixed equipment in accordance with 537.2

    The oven (as an appliance)doesn't comply with the fixed equipment category as per examples given in the regulation



    Therefore a socket in this case needs RCD protection. However ,as you've already stated a fused spur outlet would comply with regulations.



  • Registered Users, Registered Users 2 Posts: 40 LarryBarry


    For further discussion & to follow up Meercat's last point, In 554.0 it notes except where specifically exempted in 554.4. Such outlets are not intended for general use e.g. for the connection of appliances.

    Would the note "e.g. for connection of appliances" cover the proposed installation for Oven noted above considering the socket is not intended for general use & for a connection of an appliance

    554.0 General
    Plugs and socket-outlets for industrial and similar applications are standardized according to I.S. EN 60309 in
    CENELEC member countries. They are obtainable with ratings of 16 A, 32 A, 63 A and 125 A. They are also intended
    for general use outdoors where rough usage is expected such as on construction sites and on farms.
    In certain circumstances, isolation may be required for industrial socket outlets.
    Socket-outlets for general purposes indoors shall comply with I.S. 411 or BS 1363-2 as appropriate. Such socket-outlets
    may be installed outdoors in domestic and similar locations provided they are contained in enclosures with
    a degree of protection IP 54, and provided they will not be subjected to harsh conditions or rough usage.
    Non-standard types of plugs and socket-outlets are permissible for special applications (see 554.5). Circuits
    supplying socket-outlets require protection by 30 mA RCDs except where specifically exempted in 554.4. Such
    outlets are not intended for general use e.g. for the connection of appliances.

    For agricultural and horticultural installations (Clause 705), additional requirements for RCD protection apply.



  • Registered Users, Registered Users 2 Posts: 720 ✭✭✭Hoagy


    Well I can't argue with that, so I won't try to.



  • Registered Users, Registered Users 2 Posts: 40 LarryBarry


    Meercat, What are your thoughts on below?



  • Registered Users, Registered Users 2 Posts: 4,908 ✭✭✭meercat




  • Registered Users, Registered Users 2 Posts: 40 LarryBarry


    For further discussion & to follow up Meercat's last point, In 554.0 it notes except where specifically exempted in 554.4. Such outlets are not intended for general use e.g. for the connection of appliances. 

    Would the note "e.g. for connection of appliances" cover the proposed installation for Oven noted above considering the socket is not intended for general use & for a connection of an appliance

    554.0 General
    Plugs and socket-outlets for industrial and similar applications are standardized according to I.S. EN 60309 in
    CENELEC member countries. They are obtainable with ratings of 16 A, 32 A, 63 A and 125 A. They are also intended
    for general use outdoors where rough usage is expected such as on construction sites and on farms.
    In certain circumstances, isolation may be required for industrial socket outlets.
    Socket-outlets for general purposes indoors shall comply with I.S. 411 or BS 1363-2 as appropriate. Such socket-outlets
    may be installed outdoors in domestic and similar locations provided they are contained in enclosures with
    a degree of protection IP 54, and provided they will not be subjected to harsh conditions or rough usage.
    Non-standard types of plugs and socket-outlets are permissible for special applications (see 554.5). Circuits
    supplying socket-outlets require protection by 30 mA RCDs except where specifically exempted in 554.4. Such
    outlets are not intended for general use e.g. for the connection of appliances.

    For agricultural and horticultural installations (Clause 705), additional requirements for RCD protection apply.



  • Registered Users, Registered Users 2 Posts: 4,908 ✭✭✭meercat


    I’ve nothing additional or useful to add to this other than to direct anyone else with the same query back to post #13



  • Registered Users, Registered Users 2 Posts: 40 LarryBarry


    Ok so there is no relevance that it mentions appliances? e.g. for the connection of appliances



  • Registered Users, Registered Users 2 Posts: 2,007 ✭✭✭Lenar3556


    Is there anything in the current standard which specifically prohibits RCD protection on cooker circuits? Modern hobs / ovens shouldn’t give rise to any nuisance tripping.