Problem Riello RDB Kerosene Burner

  • 18-04-2024 4:14pm
    #1
    Registered Users, Registered Users 2 Posts: 3,064 ✭✭✭


    Hi all our central heating system has been switching off over the last few days. I changed the nozzle, photo cell, electrodes and gave the baffles a good clean out.
    It started up ok and ran for about half an hour now it’s gone off and when I press the red reset button it’s almost like the motor is stalling.

    Any help much appreciated.



Comments

  • Moderators, Home & Garden Moderators Posts: 6,378 Mod ✭✭✭✭Wearb


    Might be the capacitor. Probably a proper service would be very advisable. Might save you buying unneeded parts and put it running safely and efficiently.

    Please follow site and charter rules. "Resistance is futile"



  • Registered Users, Registered Users 2 Posts: 3,064 ✭✭✭pavb2


    The burner was about 10 years old I ended up just changing the complete unit. One query though the new blast tube was smaller in length by about 50 mm.



  • Moderators, Home & Garden Moderators Posts: 6,378 Mod ✭✭✭✭Wearb


    You need to have the proper burner fitted and properly commissioned. You'd have been way better off getting your service person to sort out the previous burner.

    It's likely producing lots of carbon monoxide (we know how dangerous that is) now. I'd advise you to turn it off until properly sorted.

    Please follow site and charter rules. "Resistance is futile"



  • Registered Users, Registered Users 2 Posts: 1,372 ✭✭✭monseiur


    Your old burner is almost good as new now especially as you have fitted many new parts. Don't dump it, there's at least another 10 years left in it. Next October/November stick it up on Done Deal or similar.



  • Registered Users, Registered Users 2 Posts: 3,974 ✭✭✭jimf


    there is a possibility this burner may not be able to give the same output as your old one

    if you have a shallow combustion chamber you may get away with it



  • Advertisement
  • Registered Users, Registered Users 2 Posts: 3,064 ✭✭✭pavb2


    All ok the kw rating band is the same as the old one. I replaced the blast tube with a new one the same length today. Just waiting for my engineer to adjust air and oil settings if required and check the readings on Monday.



  • Registered Users, Registered Users 2 Posts: 3,623 ✭✭✭John.G


    This may be your type(s) below, the thermal output also depends on the combustion chamber pressure. My Riello G5X came with a T3 head, jetted with a 0.6H nozzle,

    Riello G5X (below)



  • Registered Users, Registered Users 2 Posts: 3,974 ✭✭✭jimf


    what boiler do you have



  • Registered Users, Registered Users 2 Posts: 3,064 ✭✭✭pavb2


    Not at home for a few days to check but boiler and burner were all fitted as one unit about 10 years ago. As a rough guide there are 14 radiators in the house five are less than 500 mm in length. The new burner is the 744T2K



  • Registered Users, Registered Users 2 Posts: 52 ✭✭declan b


    its a warmflow burner. your better off to leave the combustion head that came with the burner on it



  • Advertisement
  • Registered Users, Registered Users 2 Posts: 1,712 ✭✭✭Lenar3556


    It’s an RDB2.2 as used in many boilers.

    But I would put the head to suit the boiler he has.



  • Registered Users, Registered Users 2 Posts: 52 ✭✭declan b


    its a warmflow rdb2.2 short combustion head. not all rdb2.2 burners are the same.



  • Registered Users, Registered Users 2 Posts: 3,064 ✭✭✭pavb2


    The advice from the supplier was to swap the blast tube for the original one. The engineer came yesterday to check everything and left the new head which came with the burner on. All sorted now thanks for responding.



  • Moderators, Home & Garden Moderators Posts: 6,378 Mod ✭✭✭✭Wearb


    @Pavb2 Out of curiosity, what were the combustion results?

    Please follow site and charter rules. "Resistance is futile"



  • Moderators, Home & Garden Moderators Posts: 6,378 Mod ✭✭✭✭Wearb


    How do you know its a Warmflow?

    Did I miss a post?

    Please follow site and charter rules. "Resistance is futile"



  • Registered Users, Registered Users 2 Posts: 3,064 ✭✭✭pavb2


    Figures as follows

    O2 % was 4.2, CO (ppm) 37, CO2 (%) 12.4, ratio 0.0003, XS air (%) 25.1



  • Moderators, Home & Garden Moderators Posts: 6,378 Mod ✭✭✭✭Wearb


    What was the flue gas temperature? What is the make and model of the boiler. Post a pic if you like.

    Please follow site and charter rules. "Resistance is futile"



  • Registered Users, Registered Users 2 Posts: 3,064 ✭✭✭pavb2


    I’m away for a few days so will check boiler manufacturer when I’m back.

    flue temp is 68 c, inlet 21 c, net 47 c



  • Registered Users, Registered Users 2 Posts: 3,974 ✭✭✭jimf


    those settings are not good co is ok

    i would like to see the co2 nearer 11.6 at this time of year risk of sooting up



  • Registered Users, Registered Users 2 Posts: 3,974 ✭✭✭jimf


    is this a high eff boiler i presume so with this fg temp



  • Advertisement
  • Registered Users, Registered Users 2 Posts: 1,712 ✭✭✭Lenar3556


    But why do you think that? He said it’s a 744T2K which is an RDB2.2 used in various boilers. Where do warmflow come into it?



  • Registered Users, Registered Users 2 Posts: 3,974 ✭✭✭jimf


    you cant change the head from a short to a long as the nozzle will be too far back in the combustion head

    also photocell may not suit



  • Registered Users, Registered Users 2 Posts: 52 ✭✭declan b


    744T2K is a RDB2.2 short combustion head 70/90 warmflow specified burner. There is many types of rdb2.2 burners