New house UFH

  • 17-10-2023 7:55pm
    #1
    Registered Users, Registered Users 2 Posts: 2,499 ✭✭✭


    hi all

    as the title suggests, I’ve just bought a new house. ufh works but the hall and bathroom downstairs are ice cold.

    downstairs there is one thermostat in the sitting room and then the main control system in the utility room.

    Il raise it with the builder but anyone has suggestions on quick fixes let me know.



Comments

  • Registered Users, Registered Users 2 Posts: 890 ✭✭✭keno-daytrader


    Check the flow meters on the ufh manifold, make sure the cold rooms are getting flow.

    ☀️ 7.8kWp ⚡3.6kWp south, ⚡4.20kWp west



  • Registered Users, Registered Users 2 Posts: 3,623 ✭✭✭John.G


    Post the manifold flow and return temperatures and the individual, identified, loop flow rates.