Geothermal well

  • 06-04-2023 8:01pm
    #1
    Registered Users, Registered Users 2 Posts: 65 ✭✭


    Planning going through at the moment for a 2200sqft house. Exploring some ideas for heating the house. There's a recently disused domestic water well circa 90m from the house. This could be a naive question. Could this potentially be used as a ground source for geothermal? Would there be costs saved by this process?



Comments

  • Registered Users, Registered Users 2 Posts: 7,476 ✭✭✭The Continental Op


    I know of it being done but afaik it all depends on the yield of the well. In the one I know of water is pumped out of the well which taps an underground aquafer. I don't think that would work with a static low yield domestic water well.

    Wake me up when it's all over.



  • Registered Users, Registered Users 2 Posts: 21,808 ✭✭✭✭Water John


    Yes, it could. You can get a quite high COP 5/6:1. You need 3 cu metres per hour. Crowd in Galway does them I think. Google water to water heat pump. You tend to need a second borehole to take the discharge water.



  • Registered Users, Registered Users 2 Posts: 7,476 ✭✭✭The Continental Op


    Thats only 3000 litres of water but as most households would use a less than a 1000 litres a day a household well might not hold up. At the very least it needs pumping at that rate during a dry spell in the summer to test it.

    Wake me up when it's all over.



  • Moderators, Home & Garden Moderators Posts: 6,630 Mod ✭✭✭✭graememk


    If you need another hole to discharge into, prob easier to get a borehole for geo thermal?



  • Registered Users, Registered Users 2 Posts: 21,808 ✭✭✭✭Water John


    The second hole doesn't need to be very deep. Yes, you'd want to be living in an area with good underground water supply. I think it's an option that should be looked into more by rural people. Though if the house is a high BER the difference to A2W may not be worth the extra cost. Put your resources into achieving a high BER, including mechanical heat recovery ventilation.



  • Advertisement
  • Registered Users, Registered Users 2 Posts: 65 ✭✭bally2009


    Thanks for the comments of advice. Good to know that it could be an option