25000 BTU Cast Iron Radiator Supplied With 15mm Piping

  • 17-02-2023 10:03am
    #1
    Registered Users, Registered Users 2 Posts: 72 ✭✭


    Hi,

    Just wondering if it's ok to install a 25k BTU cast iron rad using 15mm pipe, or should i install 22mm?

    I found some figures in a post below....these deltaT's relate to boiler supply and return i think? But wouldn't a radiator like this supplied with 70 degree water return it at a much lower temperature (effectively extracting most of the heat carried by the water)?

    with 20 degree drop and 1.5m/sec flow you can have up to 18kw on 15mm

    with 20 degree drop and 0.3m/sec flow you can have up to 3.4kw on 15mm

    with 11 degree drop and 1.5m/sec flow only up to 10kw on 15mm

    with 11 degree drop and0.3m/sec flow only up to 2kw on 15mm



Comments

  • Registered Users, Registered Users 2 Posts: 3,623 ✭✭✭John.G


    What is the total length of the pipework, ie are you taking the flow and returns from existing 22mm piping?



  • Registered Users, Registered Users 2 Posts: 72 ✭✭lebigmacncheese


    It's got it's own supply and return from manifold under the stairs 4m away...



  • Registered Users, Registered Users 2 Posts: 3,623 ✭✭✭John.G


    If your boiler temp is 70C and if you can accept 21734btu (6.37kw) as the max rad output then you require a flowrate of 9.12LPM with dT of 10C, flow/return of 70/60C. 8M of 15mm (OD) piping will have a friction loss of ~ 1.3M so assuming rad v/v + rad loss of 1m then total = 2.3M, if you use 22mm piping then pipe loss ~ 0.25M....total loss ~ 1.25M. IMO better off with the 22mm piping otherwise you will have to run the pump at a higher head than normal but no big deal really with a sealed system but a no no with a open vented system as you are inviting vent pump over and air ingress.

    If you are happy with a rad output (max) of 18629 (5.46kw) then the total piping loss is only ~ 1.3M with 15mm piping and a dT of 20c, 70/50C flow/return



  • Registered Users, Registered Users 2 Posts: 72 ✭✭lebigmacncheese


    Thanks for the response, 15mm pipes are already in the ground so will have to make do I think.... See how it works out



  • Registered Users, Registered Users 2 Posts: 3,623 ✭✭✭John.G


    If your rad is a tallish column rad then you would be well advised to insert a flow diverter (if not supplied) as the rad might literally take hours to heat up otherwise, they look like this and cost ~ €30 and are installed at the hot side.




  • Advertisement
  • Registered Users, Registered Users 2 Posts: 72 ✭✭lebigmacncheese


    Thanks for that tip...yea its 990 tall, 6 column x 2.3m wide....



  • Registered Users, Registered Users 2 Posts: 72 ✭✭lebigmacncheese


    Ho wmany mm would this add to the pipe centres John?



Advertisement