Advertisement
If you have a new account but are having problems posting or verifying your account, please email us on hello@boards.ie for help. Thanks :)
Hello all! Please ensure that you are posting a new thread or question in the appropriate forum. The Feedback forum is overwhelmed with questions that are having to be moved elsewhere. If you need help to verify your account contact hello@boards.ie
Hi there,
There is an issue with role permissions that is being worked on at the moment.
If you are having trouble with access or permissions on regional forums please post here to get access: https://www.boards.ie/discussion/2058365403/you-do-not-have-permission-for-that#latest

Gas Boiler sizing - is 18kw enough for a 170 sqm house?

  • 23-11-2022 10:36am
    #1
    Registered Users, Registered Users 2 Posts: 171 ✭✭


    Grateful for any advice.

    Looking at ordering a gas boiler and wasn't impressed with the RGI who came out so wasn't sure how reliable his opinion was - he's recommending the install of a 24kw gas boiler system. I'm very wary of oversizing the system - I'm intending to zone the house using smart tado trv's so as a result it is extremely unlikely the heat is going to be blasting in the house non stop, more likely to specific rooms at specific times, which means a boiler that modulates lower would be better I guess?

    The house is old, draughty with solid masonry walls which I am intending to renovate in the next year (mostly external insulation), currently replacing the old single glazing windows to triple glazed as it is.

    Based on a rough rule of thumb estimate from the heat geek website attached below - if I take the worst scenario, i.e. an uninsulated draughty house, its saying the heat loss would be 170sqm*110w/M2 = 18kw at -3C. Say 3kw for hot water potentially, which would lead to a 21KW system?

    However, house will have 13 radiators, which includes 3 bathroom heated towel rads - I've sized them and it appears they'll come to 15kw if I'm generous with the sizing and so an 18kw is appropriate

    If I do go with the 24KW system and it is oversized - has it the potential to modulate down to accommodate the lower heating demand?

    Just doing the research so grateful for anyone pointing out my interpretation is completely wrong in the above if so


    Post edited by thewiseowl12 on


Comments

  • Registered Users, Registered Users 2 Posts: 11,482 ✭✭✭✭Ush1


    It depends on the minimum modulation of the boiler really. I have an Ideal 24kw and it's not great, think minimum is 5kw, I have read Viessman have a modulation ratio of 17 so are much better.



  • Registered Users, Registered Users 2 Posts: 1,667 ✭✭✭wersal gummage


    Hi,

    Not sure if any help but some of your details are similar to here.

    We have 170sq Mt, externally insulated BER B, with 14 rads.

    32kw boiler here, only put in a few years ago and that was recommended by builder and his plumber



  • Registered Users, Registered Users 2 Posts: 8,044 ✭✭✭Gusser09


    5 Bed house with 11 Rads. 140sqm.

    We have the Grant Vortex 90-120 condenser. It's a 35kw. Savage yoke. Has the Rad jumping off the wall after 5 minutes. I have also noticed a considerable drop in what we are are using on oil.



  • Registered Users, Registered Users 2 Posts: 11,482 ✭✭✭✭Ush1


    Jumping off the wall isn't good for efficiency. Needs to be a low flow temp.



  • Registered Users, Registered Users 2 Posts: 8,044 ✭✭✭Gusser09


    It isn't on for as long. Of course it's good if they are heating up quicker.



  • Advertisement
  • Registered Users, Registered Users 2 Posts: 6,129 ✭✭✭kirving


    In general, the higher the output, the less efficient a boiler will be.

    Running a 35kW (output) boiler for 1 hour, will use more fuel than running a 17.5kW for two hours. But if the house isn't well insulated, or you need it to warm up quickly after being off all day, then it's good to have the higher output of course.



  • Moderators, Home & Garden Moderators Posts: 6,383 Mod ✭✭✭✭Wearb


    "Running a 35kW (output) boiler for 1 hour, will use more fuel than running a 17.5kW for two hours."

    On the face of it that paragraph isn't true. Eg Both boilers could be running at, let's say 90%efficiency.

    In condensing boilers its the return hw temperature that has the greater influence on efficiency.

    Post edited by Wearb on

    Please follow site and charter rules. "Resistance is futile"



  • Registered Users, Registered Users 2 Posts: 11,482 ✭✭✭✭Ush1


    It might be good for reaction times but not gas usage, the boiler won't ever be condensing.



  • Registered Users, Registered Users 2 Posts: 11,482 ✭✭✭✭Ush1


    Correct. Dew point of around 55c so return needs to be lower than that.



  • Moderators, Home & Garden Moderators Posts: 6,383 Mod ✭✭✭✭Wearb


    While condensing mode is desirable, there are substantial benefits (from a condensing boiler) even when not running in condensing mode. This can be seen in the difference in flue gas temperature between a condensing (high efficiency boiler) and a standard efficiency (non condensing) boiler.

    Please follow site and charter rules. "Resistance is futile"



  • Advertisement
  • Registered Users, Registered Users 2 Posts: 171 ✭✭thewiseowl12


    In the end I went with the 18kwh boiler which means that I will have to do a good job on the insulation now. The system wouldn't be as responsive as a larger boiler in a 3 zone system but I'm hoping that by having individual room thermostats I can compensate for that.



Advertisement