Advertisement
If you have a new account but are having problems posting or verifying your account, please email us on hello@boards.ie for help. Thanks :)
Hello all! Please ensure that you are posting a new thread or question in the appropriate forum. The Feedback forum is overwhelmed with questions that are having to be moved elsewhere. If you need help to verify your account contact hello@boards.ie
Hi all! We have been experiencing an issue on site where threads have been missing the latest postings. The platform host Vanilla are working on this issue. A workaround that has been used by some is to navigate back from 1 to 10+ pages to re-sync the thread and this will then show the latest posts. Thanks, Mike.
Hi there,
There is an issue with role permissions that is being worked on at the moment.
If you are having trouble with access or permissions on regional forums please post here to get access: https://www.boards.ie/discussion/2058365403/you-do-not-have-permission-for-that#latest

Certifying New build without ESB connected

  • 31-10-2022 11:19pm
    #1
    Registered Users, Registered Users 2 Posts: 1,997 ✭✭✭


    Basically: is it possible to certify/test a new build without the ESB being connected. Can a generator be used?



Comments

  • Registered Users, Registered Users 2 Posts: 4,957 ✭✭✭kirk.


    No all you'd have is pre-connections tests on the fixed wiring (cables)

    Post connection tests to complete the cert are done with an ESB supply

    Portable Gennys hooked up to installations are an unknown quantity as far as I can see re RCDs and trip times

    The bigger TNS generators you'd be able to get proper readings I'd say matching ESBN



  • Moderators, Home & Garden Moderators, Technology & Internet Moderators, Regional East Moderators Posts: 12,603 Mod ✭✭✭✭2011


    It is the earth fault loop impedance will be different when connected to the ESB supply due to a different Ze value.



Advertisement