Private profiles - please note that profiles marked as private will soon be public. This will facilitate moderation so mods can view users' warning histories. All of your posts across the site will appear on your profile page (including PI, RI). Groups posts will remain private except to users who have access to the same Groups as you. Thread here
Some important site news, please read here. Thanks!

Thickness of Ground Floor Insulation for UFH?

  • 02-11-2021 6:22pm
    #1
    Registered Users Posts: 15 PC00123424


    Have been advised to go for 150mm PIR rigid board for ground floor insulation on the raft. Wondering if there are any possible options to go for less thick, maybe 100mm or 75, or is 150mm PIR correct?

    Thanks.



Comments

  • Moderators, Home & Garden Moderators, Science, Health & Environment Moderators Posts: 16,291 Mod ✭✭✭✭ DOCARCH


    I doubt 75mm or 100mm will give you the right u-value? For refurb I'd be going for 125mm and for new build 150mm.



  • Registered Users Posts: 15 PC00123424


    Thanks



  • Registered Users Posts: 2,146 ✭✭✭ Yellow_Fern


    There are materials that will allow you to go thinner than PIR but they are very rarely used due to cost



  • Registered Users Posts: 808 ✭✭✭ monseiur


    If new build go for 150mm - but if you have central heating pipes and other service ducts criss crossing the slab, instead of one board 150mm thick go for 2 boards 60mm and 90mm. The 60mm board will be cut to fit between pipes etc and the 90mm will go on top with staggered joints etc. - a much better job.

    M.



  • Registered Users Posts: 15 PC00123424


    Thanks for your replies. No central heating pipes or much else of anything else down there so in this case think we'll stick with the single 150mm thickness board.



  • Advertisement
  • Registered Users Posts: 1,074 ✭✭✭ Roger Mellie Man on the Telly


    For UFH you must achieve a maximum u-value of 0.15W/m2K to achieve prima facie compliance with Building Regulations.

    To determine the thickness of your chosen insulation type, you need to carry out a floor U-value calculation using the perimeter / area ratio for your particular design.