Energy efficiency- Part L and small extensions

  • 11-05-2021 9:02am
    #1
    Registered Users, Registered Users 2 Posts: 1,116 ✭✭✭


    If i got it right, the energy requirements of current Part L are relaxed for an extensions where the envelope is les than 25% of the original building envelope.


Comments

  • Registered Users, Registered Users 2 Posts: 1,116 ✭✭✭PMBC


    Excuse that last brain-f**t. That might have had some applcability ot major renovations.
    So where an extension is thermally separated from the rest of the dwelling the average U value of its elements should not exceed 1.4.? If you have very few windows it cant be that hard to achieve 1.4 with say 100mm in walls and floor and even with a flat roof 100 or 150 EPS.


  • Subscribers Posts: 42,578 ✭✭✭✭sydthebeat


    PMBC wrote: »
    Excuse that last brain-f**t. That might have had some applcability ot major renovations.
    So where an extension is thermally separated from the rest of the dwelling the average U value of its elements should not exceed 1.4.? If you have very few windows it cant be that hard to achieve 1.4 with say 100mm in walls and floor and even with a flat roof 100 or 150 EPS.

    nope

    only windows and doors can be averaged at 1.4

    the average u value allowed for each element is listed in column 2 of table 5


  • Registered Users, Registered Users 2 Posts: 1,116 ✭✭✭PMBC


    Thanks Syd. I just found notes from a course that I started but didnt progress and I had Table 5 highlighted. But it would have taken me some time to get to that point!!


  • Moderators, Society & Culture Moderators Posts: 41,573 Mod ✭✭✭✭Gumbo


    PMBC wrote: »
    Excuse that last brain-f**t. That might have had some applcability ot major renovations.
    So where an extension is thermally separated from the rest of the dwelling the average U value of its elements should not exceed 1.4.? If you have very few windows it cant be that hard to achieve 1.4 with say 100mm in walls and floor and even with a flat roof 100 or 150 EPS.

    How can it be an extension to the dwelling and thermally separated?


  • Registered Users, Registered Users 2 Posts: 1,116 ✭✭✭PMBC


    As in TGD 2019 2.1.2.5 .....extensions which are thermally separated from the adjacent spaces (original building ? PMBC) ... by wall, doors etc.