Installing outdoor double plug socket

  • 01-04-2021 8:00am
    #1
    Registered Users, Registered Users 2 Posts: 303 ✭✭


    Hi

    I would like to get an outdoor double plug socket at the front of my house.

    I was thinking of installing it directly opposite a double plug on the inside of the house so they will be back to back.

    Could I take the power from the inside plug socket to the outside socket?

    Thanks.


Comments

  • Posts: 0 [Deleted User]


    .42. wrote: »
    Hi

    I would like to get an outdoor double plug socket at the front of my house.

    I was thinking of installing it directly opposite a double plug on the inside of the house so they will be back to back.

    Could I take the power from the inside plug socket to the outside socket?

    Thanks.

    Yes you can.


  • Registered Users, Registered Users 2 Posts: 169 ✭✭serox_21


    Yes,
    But if don't know what are you doing, call an electrician.


  • Registered Users, Registered Users 2 Posts: 303 ✭✭.42.


    serox_21 wrote: »
    Yes,
    But if don't know what are you doing, call an electrician.

    Yep.

    I just wanted to confirm if its logical and allowed before I get an electrician in.


  • Registered Users, Registered Users 2 Posts: 24,644 ✭✭✭✭punisher5112


    I would suggest using a fused spur and one with a switch so you can isolate the supply when not in use.


  • Registered Users, Registered Users 2 Posts: 5,401 ✭✭✭DublinDilbert


    I would suggest using a fused spur and one with a switch so you can isolate the supply when not in use.

    I always put a double pole switch on these, as above it is useful for lots of reasons to be able to isolate the socket.


  • Advertisement
  • Registered Users, Registered Users 2 Posts: 11,467 ✭✭✭✭salmocab


    I’d say get it switched too, handy to leave it off so no one robs off you but also if you use it for lights at Christmas you can turn them on or off from inside


  • Registered Users, Registered Users 2 Posts: 303 ✭✭.42.


    For the sockets in the back garden I have a switch just inside the door that controls the power to outside. Might do the same


  • Registered Users, Registered Users 2 Posts: 12,888 ✭✭✭✭Calahonda52


    Do you not need different RCD for external sockets?

    “I can’t pay my staff or mortgage with instagram likes”.



  • Registered Users, Registered Users 2 Posts: 24,644 ✭✭✭✭punisher5112


    Do you not need different RCD for external sockets?

    No but it definitely would be a good idea to keep separate if possible and fit rcbo.


  • Registered Users, Registered Users 2 Posts: 12,888 ✭✭✭✭Calahonda52


    Thanks got my rcds and rcbo's arseways so thanks for the clarification.
    I know I have an inline one for the lawnmower

    “I can’t pay my staff or mortgage with instagram likes”.