Advertisement
If you have a new account but are having problems posting or verifying your account, please email us on hello@boards.ie for help. Thanks :)
Hello all! Please ensure that you are posting a new thread or question in the appropriate forum. The Feedback forum is overwhelmed with questions that are having to be moved elsewhere. If you need help to verify your account contact hello@boards.ie
Hi there,
There is an issue with role permissions that is being worked on at the moment.
If you are having trouble with access or permissions on regional forums please post here to get access: https://www.boards.ie/discussion/2058365403/you-do-not-have-permission-for-that#latest

Removing a radiator

  • 27-02-2021 10:32am
    #1
    Registered Users, Registered Users 2 Posts: 4,099 ✭✭✭


    Hello folks, I have previously re-tiled the bathroom floor back home and am moving onto re-tiling the walls now. I will need to remove the radiator from the wall. I have no problem with the mechanics of removing the radiator itself and putting stoppers on as have done plenty of small plumbing jobs before. I know what to expect

    However, I'm wondering if after removing the radiator will water need to be replenished to the central heating system through the boiler? Also can the heating be used ok with the radiator off? It is oil fired central heating with a Grant boiler (can provide the exact model if that's relevant).

    Many thanks in advance for all constructive input and apologies if this question has being asked previously on the forum.


Comments

  • Registered Users, Registered Users 2 Posts: 1,311 ✭✭✭youtheman


    In theory, you can remove the rad without draining down the system by just closing the valves on either side and breaking the connection between the radiator and the valve. You have to put something under the connection to collect the full contents of the radiator. I would prefer to drain down the fully system before I take off the radiator. If both valves are holding then you don't need to install blanks. If your system is vented (with a tank in the attic) then the system will automatically refill and make up for any volume loss. If it's a sealed system and if the autofill valve is open the the same will apply. If it's a sealed system with the autofill valve closed then you'll have to open it to top. Remember to add corrosion inhibitor if you drain down the system.


  • Registered Users, Registered Users 2 Posts: 2,594 ✭✭✭karlitob


    youtheman wrote: »
    In theory, you can remove the rad without draining down the system by just closing the valves on either side and breaking the connection between the radiator and the valve. You have to put something under the connection to collect the full contents of the radiator. I would prefer to drain down the fully system before I take off the radiator. If both valves are holding then you don't need to install blanks. If your system is vented (with a tank in the attic) then the system will automatically refill and make up for any volume loss. If it's a sealed system and if the autofill valve is open the the same will apply. If it's a sealed system with the autofill valve closed then you'll have to open it to top. Remember to add corrosion inhibitor if you drain down the system.

    Good info here. I’m thinking about changing the type and position of my radiators in a few rooms. I’ve a sealed system (at least I think i do) and a flexicom 18k boiler. Is it straightforward enough to drain the system? I’ve no drain cock on the lowest rad. Thanks in advance.


  • Registered Users, Registered Users 2 Posts: 2,594 ✭✭✭karlitob


    karlitob wrote: »
    Good info here. I’m thinking about changing the type and position of my radiators in a few rooms. I’ve a sealed system (at least I think i do) and a flexicom 18k boiler. Is it straightforward enough to drain the system? I’ve no drain cock on the lowest rad. Thanks in advance.

    Any advice on this? Thank you.


  • Registered Users, Registered Users 2 Posts: 800 ✭✭✭niallers1


    You'll probably need to repressurize after you out the new radiator back on.


Advertisement