Boiler is lighting for upstairs, but not downstairs

  • 07-02-2021 8:38am
    #1
    Registered Users, Registered Users 2 Posts: 220 ✭✭


    I've an Ariston e Combi evo gas boiler and its lighting for upstairs, but not downstairs there are 2 separate switches.

    I've done the reset a few times, I've turned the temperature right up on the system the but the boiler is not calling for heat when i turn on the downstairs switch.

    the pressure is fine, I left the power off overnight in the hope that it may reset itself

    Also there are no error messages

    Is there any quick fix or anything i can do or is this a job for a plumber, i read online about a zone valve i cant find it in the manual.

    I'm guessing its that or the thermostat

    Thanks


Comments

  • Registered Users, Registered Users 2 Posts: 4,828 ✭✭✭meercat


    There’s a zone valve(possibly in your hot press or adjacent to the boiler)
    On the side of this there’s a manual override lever that can be slid across and latched into the open position


  • Registered Users, Registered Users 2 Posts: 23 soccermad1


    jacknife wrote:
    Is there any quick fix or anything i can do or is this a job for a plumber, i read online about a zone valve i cant find it in the manual.


    Same thing happened me it was the zone valve.. One under the sink usually for downstairs. One in hot press for upstairs.. Its a plumber job.. Replacement valve was 50 euro.


  • Registered Users, Registered Users 2 Posts: 17 Tarant


    I had a brocken Valve motor which made the burner run all the time ( to my specified temperature). Got an electrican to find out which one. Replaced it myself without hassel. Just an electric connection and screw it onto the valve


  • Registered Users, Registered Users 2 Posts: 220 ✭✭jacknife


    Thanks everyone

    Sorted the problem, i was studying the boiler manual and say about the thermostat, then i remembered the thermostat behind the curtain and it was turned down to the lowest, turned it up and the boiler lighted up