UFH connected to open vented system

  • 06-02-2021 10:45pm
    #1
    Registered Users, Registered Users 2 Posts: 51 ✭✭


    Can anyone advise if underfloor heating can be connected to an oil fired open vented system.


Comments

  • Registered Users, Registered Users 2 Posts: 1,114 ✭✭✭freddyuk


    Yes of course. You may need a mixer valve to control the temperature which should be lower than normal rad circuit or have the whole system running lower and install larger rads and TRV's and zoning etc. if the system is already old.
    If the boiler requires a set high temperature to run then you will need to have a control valve such as RAV K or similar and have dual temperatures.