Firebird with cold rads

  • 01-01-2021 9:41pm
    #1
    Registered Users, Registered Users 2 Posts: 833 ✭✭✭


    Hi all, I switched on the firebird in a property today that has been vacant for about 6 months following building works. Firebird came on straight away, circulation pump came on and ran but rads remain cold. I can hear circulation pump humming so I'm sure it's running. Building work was a refurb of ground floor including replacing two rads, one in kitchen, one in bathroom upstairs. Water had been turned off as property was vacant, only put back on as needed. Water was back on today before I ran the firebird.

    Am I missing something obvious ?

    Any and all advice welcomed.


Comments

  • Registered Users, Registered Users 2 Posts: 737 ✭✭✭holly8


    westgolf wrote: »
    Hi all, I switched on the firebird in a property today that has been vacant for about 6 months following building works. Firebird came on straight away, circulation pump came on and ran but rads remain cold. I can hear circulation pump humming so I'm sure it's running. Building work was a refurb of ground floor including replacing two rads, one in kitchen, one in bathroom upstairs. Water had been turned off as property was vacant, only put back on as needed. Water was back on today before I ran the firebird.

    Am I missing something obvious ?

    Any and all advice welcomed.

    Airlocked? Did boiler burner fire up?


  • Registered Users, Registered Users 2 Posts: 24,644 ✭✭✭✭punisher5112


    Bleed the rads to see.

    Is it water fed or pressure system?

    Could a valve be turned off?

    Is it firing for long or cutting out?

    Check rads are turned on. System may need to be balanced depending if hear gets to them all....


  • Registered Users, Registered Users 2 Posts: 3,623 ✭✭✭John.G


    If pressurised system check system pressure > 1 bar. If open vented system check water level in small header tank in attic.
    Vent the circ pump (if possible) and the boiler by slowly turning the PRV (safety valve) red knob slowly anticlockwise until air/water.
    Do not run boiler until checked out.


  • Registered Users, Registered Users 2 Posts: 833 ✭✭✭westgolf


    holly8 wrote: »
    Airlocked? Did boiler burner fire up?

    Boiler came on straight away no issue.


  • Registered Users, Registered Users 2 Posts: 833 ✭✭✭westgolf


    John.G wrote: »
    If pressurised system check system pressure > 1 bar. If open vented system check water level in small header tank in attic.
    Vent the circ pump (if possible) and the boiler by slowly turning the PRV (safety valve) red knob slowly anticlockwise until air/water.
    Do not run boiler until checked out.

    Ok, will be back there today. No header tank in attic, just small cylinder type of yoke. Will check the pressure on that. Will also try the PRV valve. Did notice last evening that the output pipe from the boiler was hot to touch on section from edge of firebird to Circulation pump.


  • Advertisement
  • Registered Users, Registered Users 2 Posts: 833 ✭✭✭westgolf


    westgolf wrote: »
    Ok, will be back there today. No header tank in attic, just small cylinder type of yoke. Will check the pressure on that. Will also try the PRV valve. Did notice last evening that the output pipe from the boiler was hot to touch on section from edge of firebird to Circulation pump.

    An update.. pressure Valve on attic cylinder was turned to zero (off) turned it back on steady at 2 bar now.


  • Registered Users, Registered Users 2 Posts: 833 ✭✭✭westgolf


    westgolf wrote: »
    An update.. pressure Valve on attic cylinder was turned to zero (off) turned it back on steady at 2 bar now.

    Update no. 2
    Pressure dropped down to about 1.5 bar after about 15 mins. Went back to firebird and spotted steam and a trickle of water from PRV Valve where it's fitted beside boiler. Looks like my valve or it's fitting is perished.


  • Registered Users, Registered Users 2 Posts: 3,623 ✭✭✭John.G


    It will probably need renewing, just keep turning the red knob slowly anticlockwise to make the valve open and snap shut a few times it might just reseat it, worth a try anyhow.


  • Registered Users, Registered Users 2 Posts: 833 ✭✭✭westgolf


    John.G wrote: »
    It will probably need renewing, just keep turning the red knob slowly anticlockwise to make the valve open and snap shut a few times it might just reseat it, worth a try anyhow.

    Thanks John G.
    It's a green twist valve, see pic, the trickle is from where the valve is "seated" in the pipe so I think that it's not sealed totally or the seal has failed ?


  • Registered Users, Registered Users 2 Posts: 833 ✭✭✭westgolf


    Can't post pic as boards saying too big


  • Advertisement
  • Registered Users, Registered Users 2 Posts: 24,644 ✭✭✭✭punisher5112


    westgolf wrote: »
    Can't post pic as boards saying too big

    If you don't have a resize app send to someone on WhatsApp and then use the pic from the WhatsApp images section. It will be resized and fit.

    Great you got it working


  • Registered Users, Registered Users 2 Posts: 833 ✭✭✭westgolf


    Picture of valve