Advertisement
If you have a new account but are having problems posting or verifying your account, please email us on hello@boards.ie for help. Thanks :)
Hello all! Please ensure that you are posting a new thread or question in the appropriate forum. The Feedback forum is overwhelmed with questions that are having to be moved elsewhere. If you need help to verify your account contact hello@boards.ie
Hi there,
There is an issue with role permissions that is being worked on at the moment.
If you are having trouble with access or permissions on regional forums please post here to get access: https://www.boards.ie/discussion/2058365403/you-do-not-have-permission-for-that#latest

Fitting CTs to a distribution panel which has an autostart standby generator.

  • 18-12-2020 11:26am
    #1
    Registered Users, Registered Users 2 Posts: 12,888 ✭✭✭✭


    1: Hope you all have a great festive season and thank you for all the contributions here in 2020. :)
    2: Have a project where a meter needs to be fitted to the incomer in a number of buildings that have mission critical IT systems with an autostart standby generator which will click in as soon as the power is cut to the main distribution board.
    3: the meter will collect 15 minute data and the plan is to fit CTs to the three phases.

    Any thoughts on how it is done?

    Thanks as always.

    “I can’t pay my staff or mortgage with instagram likes”.



Comments

  • Moderators, Home & Garden Moderators, Technology & Internet Moderators, Regional East Moderators Posts: 12,641 Mod ✭✭✭✭2011


    Are they split core CT’s ?

    Unless it is the mV type it is dangerous to leave the secondary side open circuit.
    Look into this carefully.


  • Registered Users, Registered Users 2 Posts: 12,888 ✭✭✭✭Calahonda52


    2011 wrote: »
    Are they split core CT’s ?

    Unless it is the mV type it is dangerous to leave the secondary side open circuit.
    Look into this carefully.

    Thanks, will make sure we get a RECI that knows about this stuff.

    “I can’t pay my staff or mortgage with instagram likes”.



  • Closed Accounts Posts: 91 ✭✭Yuser.


    Your average Rec won't do much with metering

    A lot depends on a site survey, CTs can prob be fitted at the main board or sub boards depending on space


  • Registered Users, Registered Users 2 Posts: 12,888 ✭✭✭✭Calahonda52


    Yuser. wrote: »
    Your average Rec won't do much with metering

    A lot depends on a site survey, CTs can prob be fitted at the main board or sub boards depending on space

    On your second point, if the generator comes on and the breaker to the good is open stopping power from generator going back onto the grid, will the entire distribution panel not be live.?

    What I am trying to get to is if the IT folk say you cant shut it down, then we cant fit the CTs.

    The two offerings are Schneider split cores and Rogowski coils.

    “I can’t pay my staff or mortgage with instagram likes”.



  • Closed Accounts Posts: 91 ✭✭Yuser.


    On your second point, if the generator comes on and the breaker to the good is open stopping power from generator going back onto the grid, will the entire distribution panel not be live.?

    What I am trying to get to is if the IT folk say you cant shut it down, then we cant fit the CTs.

    The two offerings are Schneider split cores and Rogowski coils.

    I'm not familiar with CTs
    https://www.se.com/ng/en/faqs/FA107472/

    Says there you don't need to switch off

    Whether that's true when you get to the job is another story

    It looks like the split-core is specifically designed for your application( installation needs to remain energized)


  • Advertisement
  • Closed Accounts Posts: 91 ✭✭Yuser.


    On your second point, if the generator comes on and the breaker to the good is open stopping power from generator going back onto the grid, will the entire distribution panel not be live.?

    What I am trying to get to is if the IT folk say you cant shut it down, then we cant fit the CTs.

    The two offerings are Schneider split cores and Rogowski coils.

    If you have standby generator and Dso supply

    Panels will be live unless you cut the power

    This is a specialist job anyhow. The metering installers will be familiar with this work and what way to do it


Advertisement