RCD Circuit Tripping

Options
  • 13-12-2020 1:42pm
    #1
    Registered Users Posts: 285 ✭✭


    Hi,
    I have tried to navigate the threads on this, but could not find one that matches my issue.
    I have an issue with an internal 11 plug outlet circuit that is somehow tripping with no load or plug in place. After some initial fault finding, I managed to get it to a particular circuit and have removed all plugs. So far, I have checked 4 of the plugs that they seem fine, ie all wires are connected.
    We got a full re-wire about 9 years ago.
    Any suggestions?
    Thanks


Comments

  • Closed Accounts Posts: 134 ✭✭Henryq.


    If everything is actually removed from the circuit?

    Next step really is testing the wiring and the RCD


  • Registered Users Posts: 4,733 ✭✭✭meercat


    Make sure the immersion is switched off


  • Registered Users Posts: 285 ✭✭Gavin1


    Henryq. wrote: »
    If everything is actually removed from the circuit?

    Next step really is testing the wiring and the RCD

    The circuit from what I can see is these 11 plug outlet with approx 7 on outside walls and the ones I checked seem dry.

    There is no immerison on this circuit. But I have turned it off at the switch.

    Need to wait for Ronaldo to finish FIFA game first before retrying everything again.

    Is cable and RCD testing is routine enough for an electrician?


  • Registered Users Posts: 285 ✭✭Gavin1


    With immerision off, it is still tripping


  • Closed Accounts Posts: 134 ✭✭Henryq.


    Gavin1 wrote: »

    Is cable and RCD testing is routine enough for an electrician?
    Check RCD leakage
    Check load on final circuit
    Check RCD trip times
    Disconnect final circuit
    IR test final circuit


    Something like that for your problem


  • Advertisement
  • Registered Users Posts: 285 ✭✭Gavin1


    Henryq. wrote: »
    Check RCD leakage
    Check load on final circuit
    Check RCD trip times
    Disconnect final circuit
    IR test final circuit


    Something like that for your problem

    Thanks for this. I have a multimeter!

    I remember this testing being carried out after the rewiring and got a cert to sa we where good to go.

    I take it that this is not a Sunday afternoon "give it a lash fix", unless I am an electrican?


  • Registered Users Posts: 4,733 ✭✭✭meercat


    The rcd will most likely cover all sockets in the installation

    Make sure everything is unplugged throughout the house

    Make sure heating system is turned off

    Make sure all outside sockets are unplugged

    Check all washing machine/dishwasher appliances etc are unplugged

    Check your immersion is definitely turned off


  • Registered Users Posts: 285 ✭✭Gavin1


    Seem to have found it.

    An external plug is wired to an interior plug. Did not know that !

    Opened the external plug box and it seemed damp, almost sweating. Changed the face of the plug and seems stable for now!!!

    Thanks for the help.


  • Registered Users Posts: 2,034 ✭✭✭Cerco


    Gavin1 wrote: »
    Seem to have found it.

    An external plug is wired to an interior plug. Did not know that !

    Opened the external plug box and it seemed damp, almost sweating. Changed the face of the plug and seems stable for now!!!

    Thanks for the help.
    Assume you mean socket not plug.
    You need to find out where the dampness is getting in on the outside socket. Are they proper external sockets?
    You should also determine if the internal socket is supplying the outside one.


  • Registered Users Posts: 24,647 ✭✭✭✭punisher5112


    If worried about this continuing I'd recommend getting outside on its own circuit.