heating excess to a different zone

  • 14-11-2020 10:55pm
    #1
    Registered Users, Registered Users 2 Posts: 8,593 ✭✭✭


    We have a stove with boiler. The central heating is split into two zones, day rooms and bedrooms.
    When the stove heats the water fully, the bedrooms zone gets the excess.
    Is there any way I could get the second day room to get some of this excess heat without a lot of work?


Comments

  • Registered Users, Registered Users 2 Posts: 429 ✭✭Blowheads


    We have a stove with boiler. The central heating is split into two zones, day rooms and bedrooms.
    When the stove heats the water fully, the bedrooms zone gets the excess.
    Is there any way I could get the second day room to get some of this excess heat without a lot of work?

    Are you sure it's just zone 1 that's getting the heat?
    A good stove setup would be heat the tank, tank hot pump out to the rad in all zones, kind of a safety thing also in case any one zone overheats.
    If the stove is on a while do any rads downstairs warm?
    It also would be trickier just to specify one room downstairs to get heat as opposed to the whole zone

    Best advice to ring a plumber who can quote for any work required


  • Moderators, Home & Garden Moderators Posts: 6,378 Mod ✭✭✭✭Wearb


    We have a stove with boiler. The central heating is split into two zones, day rooms and bedrooms.
    When the stove heats the water fully, the bedrooms zone gets the excess.
    Is there any way I could get the second day room to get some of this excess heat without a lot of work?
    Does this happen even if the thermostat on the second zone is calling for heat?

    Please follow site and charter rules. "Resistance is futile"



  • Registered Users, Registered Users 2 Posts: 8,593 ✭✭✭funkey_monkey


    Wearb wrote: »
    Does this happen even if the thermostat on the second zone is calling for heat?

    The thermostat for the day room doesn't activate.
    If it did then the traitors in the room with stove would come on too. As the thermostat is in hallway the radiators in the room with stove would come on too.


  • Moderators, Home & Garden Moderators Posts: 6,378 Mod ✭✭✭✭Wearb


    The thermostat for the day room doesn't activate.
    If it did then the traitors in the room with stove would come on too. As the thermostat is in hallway the radiators in the room with stove would come on too.
    Then you could put a TRV on the rad in the stove room and leave the hall stat calling for heat.

    Please follow site and charter rules. "Resistance is futile"



  • Registered Users, Registered Users 2 Posts: 8,593 ✭✭✭funkey_monkey


    Wearb wrote: »
    Then you could put a TRV on the rad in the stove room and leave the hall stat calling for heat.

    There would need to be something in the controls I set to turn on the day rooms zone thermostat? The hall start doesn't call for heat currently only the bed rooms stat.


  • Advertisement
  • Moderators, Home & Garden Moderators Posts: 6,378 Mod ✭✭✭✭Wearb


    There would need to be something in the controls I set to turn on the day rooms zone thermostat? The hall start doesn't call for heat currently only the bed rooms stat.

    So what does it do?

    Please follow site and charter rules. "Resistance is futile"



  • Registered Users, Registered Users 2 Posts: 8,593 ✭✭✭funkey_monkey


    Wearb wrote: »
    So what does it do?

    The central heating can turn on both or either zones. Central heating can only work if the hot water is turned on too.

    The stove heats the tank. When the tank reaches a preset temperature the excess heat is pumped around zone 2 - bedrooms.
    Zone 1, day rooms does not get switched on.

    There is something in the controls which only switches on zone 2 when the tank temp is reached.


  • Moderators, Home & Garden Moderators Posts: 6,378 Mod ✭✭✭✭Wearb


    The central heating can turn on both or either zones. Central heating can only work if the hot water is turned on too.

    The stove heats the tank. When the tank reaches a preset temperature the excess heat is pumped around zone 2 - bedrooms.
    Zone 1, day rooms does not get switched on.

    There is something in the controls which only switches on zone 2 when the tank temp is reached.
    But if zone 1 stat is turned up and excess heat is getting pumped around zone 2, does zone 1 not heat too?

    Please follow site and charter rules. "Resistance is futile"



  • Registered Users, Registered Users 2 Posts: 8,593 ✭✭✭funkey_monkey


    No - only zone 2 (bedrooms) switch on.


  • Moderators, Home & Garden Moderators Posts: 6,378 Mod ✭✭✭✭Wearb


    No - only zone 2 (bedrooms) switch on.
    Ok. Most likely wired conventionally with a variation for excess heat. Also likely that everything is connected in the hot press, if so an electrician would have no trouble doing what you need.

    Please follow site and charter rules. "Resistance is futile"