Using a type k thermocouple on a copper pipe

Options
  • 14-11-2020 2:18pm
    #1
    Registered Users Posts: 968 ✭✭✭


    Just a quick one if anyone can help. I want to measure the temperature of the water output of the oil burner. If I place a type k thermocouple directly on the copper pipe or the brass fittings will there be any corrosion issues? I have some spare thermocouples and transmitters that I can connect to my PLC to log the temperature if it’s unlikely to cause any issues.


Comments

  • Registered Users Posts: 1,052 ✭✭✭Tuco88


    The type I used before had a jubilee clip on it, and I used to put some thermal paste on too. Never caused any damage.

    You could use a small bit of manifold/brake caliper paint as a barrier, it shouldn't make any major difference to the measurement.


  • Moderators, Home & Garden Moderators, Technology & Internet Moderators, Regional East Moderators Posts: 12,558 Mod ✭✭✭✭2011


    I wouldn’t use a thermocouple for this purpose. They are more suited to far higher temperature ranges. For this application I would recommend a PT100.

    Anyway to answer your question it will be fine.


  • Registered Users Posts: 968 ✭✭✭medoc


    2011 wrote: »
    I wouldn’t use a thermocouple for this purpose. They are more suited to far higher temperature ranges. For this application I would recommend a PT100.

    Anyway to answer your question it will be fine.


    Thanks for the replies. Yea I’ll use the thermocouples as those are what I have for now. I might replace them for PT100 if I need to all I’ll need to do is reprogram the PR transmitters. There’s no real reason for doing this, just for a bit of fun and to add the info to my system.


  • Moderators, Home & Garden Moderators, Technology & Internet Moderators, Regional East Moderators Posts: 12,558 Mod ✭✭✭✭2011


    You will find that the PT100’s will provide a far more stable and accurate reading.
    Response time is increased but will still be very rapid. Normally thermocouples are used for far higher temperature ranges.