Terminal connection 25sq

  • 31-10-2020 8:37pm
    #1
    Registered Users, Registered Users 2 Posts: 10


    Hello,is there a terminal block you could get big enough for 25sq swa to terminate in a s fuse board.


Comments

  • Registered Users, Registered Users 2 Posts: 203 ✭✭ptogher14


    You will get any size terminal block. 25sq won't be a problem. Would a reducing pin be of benefit?


  • Closed Accounts Posts: 225 ✭✭JimToken


    What's the application

    25sq isn't that big , the board should accomodate it if it's rated for 25


  • Registered Users, Registered Users 2 Posts: 10 Rodge84


    JimToken wrote: »
    What's the application

    25sq isn't that big , the board should accomodate it if it's rated for 25

    For powering a shed on a farm.Got a schnieder ip 65 board thinking their would be space in the terminal connection for the the 25sq.


  • Registered Users, Registered Users 2 Posts: 203 ✭✭ptogher14


    I'm assuming the earth and neutral are too big for the earth and neutral bars? A reducing pin would suffice.

    Another option would be to install 25sq din rails, terminate the cable and come out in flexible tails.


  • Registered Users, Registered Users 2 Posts: 10 Rodge84


    ptogher14 wrote: »
    I'm assuming the earth and neutral are too big for the earth and neutral bars? A reducing pin would suffice.

    Another option would be to install 25sq din rails, terminate the cable and come out in flexible tails.

    Yeah,The earth and neutral are to big,I should of checked the board before purchasing.Think the din rails could be the way to go and come out with flexi as you said.Would 16s flexi be an option


  • Advertisement
  • Registered Users, Registered Users 2 Posts: 203 ✭✭ptogher14


    It's not an uncommon problem. Double check all the terminals. Sometimes there's one larger than the rest. What size breaker is protecting the 25sq? 16sq tri rated flex is good for a 100A


  • Registered Users, Registered Users 2 Posts: 10 Rodge84


    ptogher14 wrote: »
    It's not an uncommon problem. Double check all the terminals. Sometimes there's one larger than the rest. What size breaker is protecting the 25sq? 16sq tri rated flex is good for a 100A

    As the 25sq would be going on an 80 amp breaker


  • Registered Users, Registered Users 2 Posts: 203 ✭✭ptogher14


    See data sheet for tri rated flexi


  • Registered Users, Registered Users 2 Posts: 10 Rodge84


    ptogher14 wrote: »
    See data sheet for tri rated flexi

    Thats handy.Thanking you for that


  • Advertisement
  • Closed Accounts Posts: 225 ✭✭JimToken


    I remember going back a bit my inspector wanted the main protective conductor spread across 2 terminals

    Something to do with the risk of 1 terminal loosening

    I'm nearly sure he said there was a regulation but I don't see anything in ET101


  • Registered Users, Registered Users 2 Posts: 1,054 ✭✭✭Tuco88


    I think hes looking at consumer units too much. I see in what he is trying to achieve.

    Not a regulation, can't be done in most cases. Can't be done on Atex equipment.