Wiring a smart thermostat

Options
  • 18-10-2020 9:57am
    #1
    Registered Users Posts: 7,761 ✭✭✭


    Put this in the elec forum but might be better here

    Hi all changing out a 240v thermostat for a smart thermostat. Just wanted to check my approach. The smart thermostat has a four teeminals - L and N for power. There's also 2 dry contact terminals- presuming I just loop the L to the L on the switched contact to switch the boiler on and off when the thermo asks for it?


Comments

  • Hosted Moderators Posts: 3,496 ✭✭✭DGOBS


    Would need a little more detail, what way is your current stat wired (and do you have a timer also?)
    What brand smart stat you using.


  • Registered Users Posts: 7,761 ✭✭✭Pinch Flat


    DGOBS wrote: »
    Would need a little more detail, what way is your current stat wired (and do you have a timer also?)
    What brand smart stat you using.

    Thanks for the reply

    I have a danfoss timer that does both hot water and central heating

    https://images.app.goo.gl/XEiKfiA3bdSe1CNf7

    Current stat is a danfoss as well

    https://images.app.goo.gl/opYFxvf5rMksqaQB7

    Live and neutral wired to back of the thermo stat


  • Registered Users Posts: 7,761 ✭✭✭Pinch Flat


    DGOBS wrote: »
    Would need a little more detail, what way is your current stat wired (and do you have a timer also?)
    What brand smart stat you using.

    Thanks for the reply

    I have a danfoss timer that does both hot water and central heating

    https://images.app.goo.gl/XEiKfiA3bdSe1CNf7

    Current stat is a danfoss as well

    https://images.app.goo.gl/opYFxvf5rMksqaQB7

    Live and neutral wired to back of the thermo stat


  • Hosted Moderators Posts: 3,496 ✭✭✭DGOBS


    So your replacing the time correct (and looping out the stat?)

    What are you installing?


  • Registered Users Posts: 7,761 ✭✭✭Pinch Flat


    DGOBS wrote: »
    So your replacing the time correct (and looping out the stat?)

    What are you installing?

    Keeping the danfoss timer and putting in a new smart stat where the thermostat is. Or do I just swap out the timer altogether?

    Edit its one of these

    https://www.amazon.co.uk/MOES-Thermostat-Temperature-Controller-Electric/dp/B07PKQ75DG


  • Advertisement
  • Moderators, Home & Garden Moderators Posts: 6,215 Mod ✭✭✭✭Wearb


    Normally you would replace both with your new stat, which has a built in timer. Yes it's most likely that you would loop 4 to 1. I say most likely as I'm not there to see the installation. I presume 4 is coming from a fused spur.

    I am only familiar with oil systems. If this is gas, there might be other considerations that I'm unaware of. So proceed with caution.

    Please follow site and charter rules. "Resistance is futile"



  • Hosted Moderators Posts: 3,496 ✭✭✭DGOBS


    Original controller is 2 channel (separate hot water) so not enough just to change the stat


  • Moderators, Home & Garden Moderators Posts: 6,215 Mod ✭✭✭✭Wearb


    He could leave the hot water on the programmer and just control the heat with new stat.
    Last hive I installed, I wired it in parallel with existing programmer. I didn't have faith in the couple being able to quickly grasp the usage of the new stat.

    Please follow site and charter rules. "Resistance is futile"



  • Registered Users Posts: 7,761 ✭✭✭Pinch Flat


    Thanks for the help guys. Sounds a little more complicated than I'd anticipated. :)

    Wondering would one solution be to leave the central heating side "on" permanently on the existing danfoss timer and use the new stat for timing on / off for the boiler to provide hot water to the central heating circuit. As far as I know I can programme the hot water separately on the existing panel as the hot water / central heating circuit is separated.


  • Moderators, Home & Garden Moderators Posts: 6,215 Mod ✭✭✭✭Wearb


    Pinch Flat wrote: »
    Thanks for the help guys. Sounds a little more complicated than I'd anticipated. :)

    Wondering would one solution be to leave the central heating side "on" permanently on the existing danfoss timer and use the new stat for timing on / off for the boiler to provide hot water to the central heating circuit. As far as I know I can programme the hot water separately on the existing panel as the hot water / central heating circuit is separated.
    That should work (assuming you have a normal S plan system).

    Please follow site and charter rules. "Resistance is futile"



  • Advertisement
  • Registered Users Posts: 7,761 ✭✭✭Pinch Flat


    What you reckon on the live to pin 1. Makes sense in that the neutral and live wired to the live and neutral terminals alone just provides power and no switching ability - I could hear the thermostat click on and off when I programmed it but no movement on the heat.


  • Registered Users Posts: 292 ✭✭wizardman


    Did you get the single channel? IE Heating only?


  • Moderators, Home & Garden Moderators Posts: 6,215 Mod ✭✭✭✭Wearb


    Pinch Flat wrote: »
    What you reckon on the live to pin 1. Makes sense in that the neutral and live wired to the live and neutral terminals alone just provides power and no switching ability - I could hear the thermostat click on and off when I programmed it but no movement on the heat.
    1 and 2 are the switching contacts. 3 and 4 are "permanent" live and neutral. Run a jumper from 1 to 4. All assuming it's already wired in a conventional manner.

    Please follow site and charter rules. "Resistance is futile"



  • Registered Users Posts: 7,761 ✭✭✭Pinch Flat


    okay so a bit more time with the BH weekend an a 5km lock down since i posted last :) So the original thermostat was a Flash one, link here: https://www.rvr.ie/products/room-thermostat-1
    I wasn't convinced it did work in regulating temperature, but it did click the boiler on and off if you turned the dial.

    When I had the boiler replaced a few years back, the guy that did it put in motorised valves in the hot press a so the heating system and hot water is operated separately.

    he left back a Danfoss thermostat that was never fitted - this is the one I fitted last weekend to see if I could get some control over the boiler. I now realise it's a 3 wire one, so the boiler is operating but the thermostat is not controlling it. It does click when you turn the dial, but it's obviously not switching the boiler. It is possible to get a 2 wire set up work with 3 wire thermostat by linking Live to Comm?

    Photos of both set ups attached. First two images are the Flash, Third is how I wired up the Danfoss Thermostat and the last is my proposed wiring of the new smart stat. I realise my colours are mixed up in the photo :o


  • Moderators, Home & Garden Moderators Posts: 6,215 Mod ✭✭✭✭Wearb


    What happened to the thermostat that you linked to earlier?

    Please follow site and charter rules. "Resistance is futile"



  • Registered Users Posts: 7,761 ✭✭✭Pinch Flat


    Wearb wrote: »
    What happened to the thermostat that you linked to earlier?

    which one - the flash or the danfoss?


  • Moderators, Home & Garden Moderators Posts: 6,215 Mod ✭✭✭✭Wearb


    Pinch Flat wrote: »
    which one - the flash or the danfoss?
    529742.jpgThis one?

    Please follow site and charter rules. "Resistance is futile"



  • Registered Users Posts: 7,761 ✭✭✭Pinch Flat


    Haven't wired this in yet - the fourth image i linked above (ignore my marked up colours in the wiring :)) are how I was going to wire it up.


  • Moderators, Home & Garden Moderators Posts: 6,215 Mod ✭✭✭✭Wearb


    I am now mixed up and not sure what you want to know.

    Please follow site and charter rules. "Resistance is futile"



  • Registered Users Posts: 7,761 ✭✭✭Pinch Flat


    okay sorry - will remove the new wiring diagram I marked up for my Moes - I've marked this up incorrectly.


  • Advertisement
  • Registered Users Posts: 7,761 ✭✭✭Pinch Flat


    Okay so here's the mark up of the new moes stat I'm going to fit. The original stat was a flash one, wired up as the first photo in my post from earlier today


  • Moderators, Home & Garden Moderators Posts: 6,215 Mod ✭✭✭✭Wearb


    Pinch Flat wrote: »
    Okay so here's the mark up of the new moes stat I'm going to fit. The original stat was a flash one, wired up as the first photo in my post from earlier today


    Assuming yellow is live and blue neutral, then you need a feed from from 2 to the boiler.


    As I said before, this all assumes everything else is done correctly. If you are not sure get someone who know those things to do it.

    Please follow site and charter rules. "Resistance is futile"



  • Registered Users Posts: 7,761 ✭✭✭Pinch Flat


    okay think I Might park this. I was working in the basis of a jumper from 1 to 4, but you reckon i need a feed from 2 to the boiler which I don't understand


  • Hosted Moderators Posts: 3,496 ✭✭✭DGOBS


    You are barking up the wrong tree.

    Look at your current stat pictures, and that is not a live an neutral, that is someone using the neutral (blue) wire as the return for live.
    So all is at the current stat is a live in, and a live out.

    What you need for the stat your intending wiring in, is 240vs live, neutral (both used to power and operate the new stat) and then a switched live in and out to the appliance (yes potentially you can loop common for this purpose, but you don't have the wiring you need to achieve what you want at the current thermostat) I can't see what you want to do working.

    the reason your old stat didn't work (properly) is it relies on an anticipator inside the stat for accuracy, but without a neutral it wouldn't work (bet the light never worked either for the same reason)

    Sorry


  • Registered Users Posts: 7,761 ✭✭✭Pinch Flat


    Ah grand thanks. those thermostats need a neutral to create some resistant and heat inside to work properly don't they?

    might have a look at the danfoss programmable controller. There's a spur beside it that a could probably get power from for the new thermostat but it's in an unheated utility room so the thermostat would be useless located there


  • Hosted Moderators Posts: 3,496 ✭✭✭DGOBS


    Why not purchase something like a HIVE, dual receiver to replace the current timer, then the stat is wireless so put hat where you like, bridge/loop out the old wired stat, and you'll have the Hive hub so you can control remotely from the app if you want.


  • Registered Users Posts: 7,761 ✭✭✭Pinch Flat


    DGOBS wrote: »
    Why not purchase something like a HIVE, dual receiver to replace the current timer, then the stat is wireless so put hat where you like, bridge/loop out the old wired stat, and you'll have the Hive hub so you can control remotely from the app if you want.

    Yeah sounds like the way to go. Thanks for the help to you and Wearb anyway