Type of RCBO on a priority unit?

  • 09-10-2020 8:59pm
    #1
    Registered Users, Registered Users 2 Posts: 9


    Hi guys

    Okay so I had a client tell me that the RCBO was tripping
    their priority unit for a shower when either shower is on. I tested both circuits and no fault came up. I inspected all terminals no damage to cables. However I did notice that the RCBO was a type B.

    Do type B MCB's and RCBO's tend to trip when supplying contractors controlling inductive loads?

    Should a type C RCBO of been used here? And should I swap the RCBO for type C?


Comments

  • Closed Accounts Posts: 13,422 ✭✭✭✭Bruthal


    Try a different rcbo


  • Registered Users, Registered Users 2 Posts: 17,189 ✭✭✭✭Sleeper12


    Different RCBO of the same type will most likely resolve the issue. Not everyone agrees but in my experience with electric showers I come across quite a few of seemingly healthy RCBOS that have become over sensitive or trip intermittently. Replacing the RCBO should resolve the issue


  • Banned (with Prison Access) Posts: 253 ✭✭Xtrail14


    Don’t use Wild Buzz in his red micra to replace it.


  • Registered Users, Registered Users 2 Posts: 9 Ninja1000


    Sleeper12 wrote: »
    Different RCBO of the same type will most likely resolve the issue. Not everyone agrees but in my experience with electric showers I come across quite a few of seemingly healthy RCBOS that have become over sensitive or trip intermittently. Replacing the RCBO should resolve the issue

    Yea that's what I did anyway. I replaced the RCBO just incase but I wasn't completely comfortable walking away without finding exactly what was causing the problem.
    I like when I find the culprit it makes me sleep better at night knowing that I won't have to go back to the house lol

    Thanks for the advice lads


  • Registered Users, Registered Users 2 Posts: 4,828 ✭✭✭meercat


    Sleeper12 wrote: »
    Different RCBO of the same type will most likely resolve the issue. Not everyone agrees but in my experience with electric showers I come across quite a few of seemingly healthy RCBOS that have become over sensitive or trip intermittently. Replacing the RCBO should resolve the issue

    I agree