Advertisement
If you have a new account but are having problems posting or verifying your account, please email us on hello@boards.ie for help. Thanks :)
Hello all! Please ensure that you are posting a new thread or question in the appropriate forum. The Feedback forum is overwhelmed with questions that are having to be moved elsewhere. If you need help to verify your account contact hello@boards.ie
Hi there,
There is an issue with role permissions that is being worked on at the moment.
If you are having trouble with access or permissions on regional forums please post here to get access: https://www.boards.ie/discussion/2058365403/you-do-not-have-permission-for-that#latest

Grant vortex overheating problem

  • 03-07-2020 10:29pm
    #1
    Registered Users, Registered Users 2 Posts: 166 ✭✭


    I recently installed a grant vortex boiler house module. Everything was fine for the first week but then the customer rang saying the boiler never cut in that morning. I called and it had went out on the high limit stat. I got some air out at the coil and everything worked fine for the next 11 days. But he rang me today saying he had the same problem. All he’s using it for at the moment is heating hot water, there are two motorised valves controlling upstairs and downstairs, it’s a sealed system, boiler stat seems to be cutting in and out fine when I turn it, new circulating pump fitted with install.... can anyone think of a reason please??


Comments

  • Moderators, Home & Garden Moderators Posts: 6,380 Mod ✭✭✭✭Wearb


    I presume pump is pumping in correct direction?
    Turn your multimeter to temp and stick the temperature wire end in the pocket to check the boiler stat.
    Does this still happen with boiler stat at lowest setting?
    Did you flush the system?
    What programme is pump set to?

    Does this have a pump overrun? It might need one.

    Just things running through my head after reading your post.

    Please follow site and charter rules. "Resistance is futile"



  • Registered Users, Registered Users 2 Posts: 3,974 ✭✭✭jimf


    make sure the 2 probes are fully inserted into the pocket on the boiler

    any comments from customer re rads/water getting super hot


  • Registered Users, Registered Users 2 Posts: 166 ✭✭hsan


    jimf wrote: »
    make sure the 2 probes are fully inserted into the pocket on the boiler

    any comments from customer re rads/water getting super hot

    Hi I had trouble getting one probe in alright because it was so tight. Ya he did say that the water was very hot even though the stat is down to the lowest. I had a laser to check the temps but I don’t think it’s very accurate


  • Registered Users, Registered Users 2 Posts: 3,974 ✭✭✭jimf


    hsan wrote: »
    Hi I had trouble getting one probe in alright because it was so tight. Ya he did say that the water was very hot even though the stat is down to the lowest. I had a laser to check the temps but I don’t think it’s very accurate


    first place to look and rule out so

    you should not have any difficulty getting probes in go back and take photo and post here


    they are usually quite loose even

    that is why I suggested thinking the run stat probe may have popped out


  • Registered Users, Registered Users 2 Posts: 166 ✭✭hsan


    So I called there today, I just changed the circulating pump to rule it out for definite. I had the stat turned down to the lowest and I had a thermometer on the flow pipe and it got to 70 degrees so I manually plugged out the burner and let the pump take the heat away. I’m going to put in a service call but do ye think that the dual stat could be faulty? When the stat is down to the lowest should it cut out below 60 degrees or there or thereabouts?


  • Advertisement
  • Registered Users, Registered Users 2 Posts: 3,974 ✭✭✭jimf


    sounds like a faulty stat run temp 55/75

    I changed one about 3 months ago on a vortex with same issue

    it can happen

    the lads in grants are sound you will have no issue with them


  • Registered Users, Registered Users 2 Posts: 166 ✭✭hsan


    jimf wrote: »
    sounds like a faulty stat run temp 55/75

    I changed one about 3 months ago on a vortex with same issue

    it can happen

    the lads in grants are sound you will have no issue with them
    Thanks Jimf
    Quick question, How old was the boiler that you changed the stat on 3 months ago?
    I only fitted this boiler about 3 weeks ago


  • Registered Users, Registered Users 2 Posts: 3,974 ✭✭✭jimf


    hsan wrote: »
    Thanks Jimf
    Quick question, How old was the boiler that you changed the stat on 3 months ago?
    I only fitted this boiler about 3 weeks ago

    only fitted a few days


  • Registered Users, Registered Users 2 Posts: 166 ✭✭hsan


    jimf wrote: »
    only fitted a few days

    The only thing that’s bugging me is the fact that it worked for 5 days and then worked for 11.
    Are grant usually good to sort out the problem themselves?


  • Registered Users, Registered Users 2 Posts: 3,974 ✭✭✭jimf


    hsan wrote: »
    The only thing that’s bugging me is the fact that it worked for 5 days and then worked for 11.
    Are grant usually good to sort out the problem themselves?

    grants are a1 just put a call in to technical on Monday


  • Advertisement
  • Registered Users, Registered Users 2 Posts: 166 ✭✭hsan


    jimf wrote: »
    grants are a1 just put a call in to technical on Monday

    Ok, thanks for the help Jimf


  • Registered Users, Registered Users 2 Posts: 3,974 ✭✭✭jimf


    hi hsan any update


  • Registered Users, Registered Users 2 Posts: 1,492 ✭✭✭roy rodgers


    Just for interest what size boiler did you install?


Advertisement