RCD tripping every three to four days

  • 11-06-2020 10:03am
    #1
    Registered Users, Registered Users 2 Posts: 1,100 ✭✭✭


    Hi all

    I've been having an ongoing problem for over a year or so now. Initially the MCB tripped but now the RCD for sockets trips (never the MCB anymore.)

    I though it was the freezer as when I'd unplug it for 12 hours, the problem would go away for about three or four days but then it would start tripping again as often as three to four times in the day until I unplug the freezer again.

    It tripped once when the freezer was not plugged in and I changed the freezer but still it tripped again after four days. So I turned off the MCB and it didn't trip for a week and a half which confirmed that it is very likely on that circuit.

    I then unplugged everything from that circuit and switched on the MCB to determine if its the circuit or something plugged in there. The RCD tripped twice this morning after only two days.

    From reading about similar problems on here, it is probably going to be either a faulty cable or MCB (unlikely).

    Whats confusing me is the way it doesn't happen for a few days and then starts to trip frequently. Could this behaviour give a hint as to the cause?


    Any ideas, greatly appreciated.


Comments

  • Registered Users, Registered Users 2 Posts: 2,637 ✭✭✭brightspark


    Damaged insulation, dampness?

    An electrician with the correct test equipment (megger) should easily find the problem.

    Alternatively visually check all the cables and connections on that circuit.


  • Registered Users, Registered Users 2 Posts: 2,010 ✭✭✭GooglePlus


    Damaged insulation, dampness?

    An electrician with the correct test equipment (megger) should easily find the problem.

    Alternatively visually check all the cables and connections on that circuit.

    What would the solution be if it was dampness? I've a similar problem to the OP, tripping RCD caused by a leak, which has since been fixed but obviously damp in behind the wall.


  • Registered Users, Registered Users 2 Posts: 2,637 ✭✭✭brightspark


    GooglePlus wrote:
    What would the solution be if it was dampness? I've a similar problem to the OP, tripping RCD caused by a leak, which has since been fixed but obviously damp in behind the wall.


    You may need to replace the cable and any thing else damaged by the water. But you should sort out the dampness first.


  • Registered Users, Registered Users 2 Posts: 4,828 ✭✭✭meercat


    I’d check that the immersion is turned off first

    The mcb tripping may just be coincidental to this issue

    Neutral to earth fault most likely

    Agree with poster who said a competent rec should find this fault with a few tests.


  • Closed Accounts Posts: 122 ✭✭Chicoso


    Shouldn't be too hard to find

    I would probably plug out the 2 wire electronic appliances

    Leave some of the other appliances in-circuit and test at 250v


  • Advertisement
  • Registered Users, Registered Users 2 Posts: 1,100 ✭✭✭Comer1


    Chicoso wrote: »
    Shouldn't be too hard to find

    I would probably plug out the 2 wire electronic appliances

    Leave some of the other appliances in-circuit and test at 250v

    Thanks, I had all appliances unplugged from the circuit and it still tripped


  • Closed Accounts Posts: 122 ✭✭Chicoso


    Comer1 wrote: »
    Thanks, I had all appliances unplugged from the circuit and it still tripped

    Unless you can nail it down you'll need a rec to test


  • Registered Users, Registered Users 2 Posts: 1,100 ✭✭✭Comer1


    Chicoso wrote: »
    Unless you can nail it down you'll need a rec to test

    Seems like that's my only option now, thanks.


  • Registered Users, Registered Users 2 Posts: 1,100 ✭✭✭Comer1


    Just to update in case this is found in a search, solved by changing the RCD.



  • Registered Users, Registered Users 2 Posts: 4,828 ✭✭✭meercat


    Cheers for the update. Did your rec do an insulation resistance test and an rcd test to confirm



  • Advertisement
  • Registered Users, Registered Users 2 Posts: 1,100 ✭✭✭Comer1


    No, we spent a month isolating different circuits and it continued to trip, so I asked him to change the rcd three months ago and it hasn't tripped since.



  • Registered Users, Registered Users 2 Posts: 4,828 ✭✭✭meercat


    That’s great.

    press the test button regularly (once a month is recommended)to ensure proper mechanical operation



  • Registered Users, Registered Users 2 Posts: 2,567 ✭✭✭Risteard81


    There's still every chance that there was an intermittent fault. It's more likely than a faulty RCD in my opinion.



  • Registered Users, Registered Users 2 Posts: 84,762 ✭✭✭✭Atlantic Dawn
    M


    I'd a similar problem, turned out to be the pump for the boiler on the way out tripping it, very difficult to diagnose, the replacement sorted it,



  • Registered Users, Registered Users 2 Posts: 1,100 ✭✭✭Comer1


    Perhaps you are correct but it was a very quick and cheap fix to change the RCD. Every search I made came back with the same opinion, very unlikely to be the RCD, so I didn't change it. Perhaps if I had followed my own (uninformed) instinct and changed it, I could have saved myself years of hassle and stress. This is why I've updated the thread, to let others know that it could be a faulty RCD.



  • Registered Users, Registered Users 2 Posts: 1,100 ✭✭✭Comer1




  • Registered Users, Registered Users 2 Posts: 1,988 ✭✭✭Andrea B.


    But has the MCB tripping been resolved? This is downline from RCD (faulty/shorted RCD should not trip MCB) and is designed to trip once its current rating exceeded.

    With this, I suspect an issue still exists. This could be a seasonal related issue or other.



  • Registered Users, Registered Users 2 Posts: 1,100 ✭✭✭Comer1


    The MCD hasn't tripped for years. That was my initial problem so I assumed that when the RCD started tripping, it was related to the MCD tripping. When the RCD started tripping instead of the MCD, I turned off that MCD but the RCD continued to trip. I know, too much of a coincidence for them not to be related but there has been no logic to this problem over the past three years. You are correct, it could be seasonal. It stopped for one winter when I only use a stove so when it started again in the summer, I thought it was the pump on the central heating. Disconnected that and it stopped so after a few weeks, I changed that. But after a while, tripping returned, even when I only used the stove. It had gotten very bad a few months ago so I started leaving MCDs off to isolate the problem. It continued to trip with every MCD off so that's when I changed the the RCD. What's a real mystery is that I have made so many changes over the past few years and the problem would go away for a while and then return. None of these changes were related so why almost all of them would have temporarily improved the situation makes no sense.

    I'm not saying it won't come back, but I'm daring to hope we have solved it, time will tell I suppose. Just to let people know that changing the RCD years ago could have saved me a lot of hassle. If it does start tripping again, I will report back and so you can say "told you so"😁



  • Registered Users, Registered Users 2 Posts: 1,988 ✭✭✭Andrea B.


    No, not a case of "i told you so".

    I like problem solving, that's why i stuck my nose in.

    +the excellent detailed history you gave, made it all the more tangible.

    Other things may have been corrected while he changed out RCD ( eg. A bad/hot terminal on MCB, causing it to trip / spreading loads from MCBs etc).

    Fingers crossed.