Earth size for trunking

  • 28-05-2020 12:20AM
    #1
    Registered Users, Registered Users 2 Posts: 12


    Doing a flat rewire and ran a new 16 T&E to a new outdoor meter cabinet. I ran it down the inside of the external wall which is battoned out, in 50mm steel trunking and bonded the trunking with a 10mm earth from MET, but wondering should it be bonded with a 16mm earth?


Comments

  • Moderators, Home & Garden Moderators, Technology & Internet Moderators, Regional East Moderators Posts: 12,682 Mod ✭✭✭✭2011


    10 mm is fine for bonding the trunking.