Odd MCB issue

  • 29-01-2020 10:54am
    #1
    Closed Accounts Posts: 1,862 ✭✭✭


    Morning,

    Noticed an odd issue with my MCBs last night - two of them which are beside each other on the board look to be linked somehow: upstairs sockets & downstairs sockets. If both or either one is up, then both circuits are live and the only way to kill them is to switch down both MCBs. Any ideas what could be the issue?


Comments

  • Closed Accounts Posts: 305 ✭✭kramer1


    Sounds like it might be a ring main split across 2 mcb s by mistake, what is the rating of the mcb s?


  • Moderators, Home & Garden Moderators, Technology & Internet Moderators, Regional East Moderators Posts: 12,641 Mod ✭✭✭✭2011


    Agreed.
    One way or another the MCBs are connected in parallel.


  • Closed Accounts Posts: 1,862 ✭✭✭un5byh7sqpd2x0


    kramer1 wrote: »
    Sounds like it might be a ring main split across 2 mcb s by mistake, what is the rating of the mcb s?

    MCBs are 10A. Is this a safety issue? If they’re in parallel is the circuit now a 20A one or somewhere in between?


  • Closed Accounts Posts: 305 ✭✭kramer1


    MCBs are 10A. Is this a safety issue? If they’re in parallel is the circuit now a 20A one or somewhere in between?

    This all sounds really wrong, I'd get a sparks out to find out what's going on.


  • Registered Users, Registered Users 2 Posts: 506 ✭✭✭Maewyn Succat


    MCBs are 10A. Is this a safety issue? If they’re in parallel is the circuit now a 20A one or somewhere in between?

    No it'll still be a 10 amp circuit. As said your best bet is to get an electrician to have a look at it because something is not right.


  • Advertisement
  • Registered Users, Registered Users 2 Posts: 17 BigVanVador


    Morning,

    Noticed an odd issue with my MCBs last night - two of them which are beside each other on the board look to be linked somehow: upstairs sockets & downstairs sockets. If both or either one is up, then both circuits are live and the only way to kill them is to switch down both MCBs. Any ideas what could be the issue?

    Yeah I agree with Kramer. Its a ring circuit that was split probably by accident when the board was replaced more than likely just needs a 20a mcb to be whacked in and the two circuits joined.


  • Closed Accounts Posts: 305 ✭✭kramer1


    How many sockets on the affected circuit?


  • Moderators, Home & Garden Moderators, Technology & Internet Moderators, Regional East Moderators Posts: 12,641 Mod ✭✭✭✭2011


    The OP has highlighted more than one wiring issue. I would expect that a half descent electrician will uncover quite a few more. I would get this looked at sooner rather than later.


  • Registered Users, Registered Users 2 Posts: 24,644 ✭✭✭✭punisher5112


    Sockets should be on a 20amp and lights on a 10amp.


  • Closed Accounts Posts: 1,862 ✭✭✭un5byh7sqpd2x0


    Sorry, my bad. They’re light circuits not sockets... 22 bulbs on downstairs circuit and 15 or so upstairs.

    The board wasn’t replaced, it was wired this way day one. The house is pretty new so only discovered this issue this week


  • Advertisement
  • Registered Users, Registered Users 2 Posts: 24,644 ✭✭✭✭punisher5112


    Are they tripping out?


  • Registered Users, Registered Users 2 Posts: 657 ✭✭✭I Am The Law


    It's what is known as an Erroneous Connection, current rules (ET101) require a test to be done on new installations and give detail on how to carry it out.

    Get your SafeElectric spark to sort it for you.


  • Closed Accounts Posts: 1,069 ✭✭✭Xertz


    This is way beyond DIY issue legally. You need to call in a professional.


  • Closed Accounts Posts: 13,422 ✭✭✭✭Bruthal


    No it'll still be a 10 amp circuit. As said your best bet is to get an electrician to have a look at it because something is not right.

    Its likely it would require well over 20 amps to trip one 10a mcb if 2 in parallel. Then the second one would quickly follow.


  • Closed Accounts Posts: 1,862 ✭✭✭un5byh7sqpd2x0


    Xertz wrote: »
    This is way beyond DIY issue legally. You need to call in a professional.

    I've no intention of trying to fix it myself, there's a sparks coming tomorrow to sort it out. I just wanted to know how dangerous this was and how much of an arse kicking I should be giving the original electrician.


  • Moderators, Home & Garden Moderators, Technology & Internet Moderators, Regional East Moderators Posts: 12,641 Mod ✭✭✭✭2011


    I've no intention of trying to fix it myself, there's a sparks coming tomorrow to sort it out.

    That’s good news. It would be prudent to get him to check the entire installation.


  • Registered Users, Registered Users 2 Posts: 566 ✭✭✭adrian92


    To answer the OP

    As others have said the load side of the MCBs have been looped.

    Remove both MCBs
    Replace with one with,I think, 20 amp rating


  • Registered Users, Registered Users 2 Posts: 566 ✭✭✭adrian92


    adrian92 wrote: »
    To answer the OP

    As others have said the load side of the MCBs have been looped.

    Remove both MCBs
    Replace with one with,I think, 20 amp rating

    Attached


  • Registered Users, Registered Users 2 Posts: 2,637 ✭✭✭brightspark


    Sorry, my bad. They’re light circuits not sockets... 22 bulbs on downstairs circuit and 15 or so upstairs.

    adrian92 wrote:
    To answer the OP

    adrian92 wrote:
    As others have said the load side of the MCBs have been looped.

    adrian92 wrote:
    Remove both MCBs Replace with one with,I think, 20 amp rating


    Did you miss the post where they said it was a lighting circuit?


  • Registered Users, Registered Users 2 Posts: 5,401 ✭✭✭DublinDilbert


    Did you miss the post where they said it was a lighting circuit?

    If it's a lighting circuit the circuits are probably joined at a light switch or two switches are joined.


  • Advertisement
  • Registered Users, Registered Users 2 Posts: 2,637 ✭✭✭brightspark


    If it's a lighting circuit the circuits are probably joined at a light switch or two switches are joined.

    I'd agree, but that isn't a reason to put them all on a single 20A MCB.


  • Registered Users, Registered Users 2 Posts: 566 ✭✭✭adrian92


    Did you miss the post where they said it was a lighting circuit?

    Yes, I missed that lighting circuits involved.

    The OP originally stated power outlets only (later said lighting circuits involved)

    Given that, I would be reluctant to give any advice .
    Seems to me a need for an electrician required here.


  • Posts: 7,712 ✭✭✭ [Deleted User]


    2011 wrote: »
    That’s good news. It would be prudent to get him to check the entire installation.

    They’d be leaving themselves open to getting fleeced then. If they’re not tripping then I’d be inclined to leave them.


  • Closed Accounts Posts: 13,422 ✭✭✭✭Bruthal


    I'd agree, but that isn't a reason to put them all on a single 20A MCB.

    Its likely he was pointing out a possible cause, not this single 20A as a solution.


  • Closed Accounts Posts: 13,422 ✭✭✭✭Bruthal


    They’d be leaving themselves open to getting fleeced then. If they’re not tripping then I’d be inclined to leave them.

    Recommending leaving 2 lighting mcbs incorrectly connected in parallel is poor imo.

    And with that level of electrical install, checking the rest of the installation is definitely good advice.


  • Moderators, Home & Garden Moderators, Technology & Internet Moderators, Regional East Moderators Posts: 12,641 Mod ✭✭✭✭2011


    They’d be leaving themselves open to getting fleeced then. If they’re not tripping then I’d be inclined to leave them.

    The idea of the MCB is to protect the connected cable from an over current condition. The way these MCBs have been connected means that they cannot provide adequate protection. Leaving circuits without proper protection is inadvisable as is concluding that the circuits are heathy just because incorrectly installed protective devices have not tripped.

    The cost of making an electrical installation safe is generally very small when compared to the value of the property. Don’t be “penny wise and pound stupid”.


  • Registered Users, Registered Users 2 Posts: 2,637 ✭✭✭brightspark


    Depending on the age of the house, if no other work was done since it was originally installed then the proper tests were not carried out for the certification.


  • Registered Users, Registered Users 2 Posts: 876 ✭✭✭TheBully


    It’s just a lighting circuit lads, remove the loop on the load side. Problem solved


  • Registered Users, Registered Users 2 Posts: 876 ✭✭✭TheBully


    Depending on the age of the house, if no other work was done since it was originally installed then the proper tests were not carried out for the certification.

    What test? It was an oversight at best


  • Advertisement
  • Closed Accounts Posts: 305 ✭✭kramer1


    TheBully wrote: »
    What test? It was an oversight at best

    Erroneous test,but it might not been around at the time, and visual inspection if there's 1.5s going into a 20a breaker