New gas boiler query

  • 24-01-2020 10:25pm
    #1
    Registered Users, Registered Users 2 Posts: 3,097 ✭✭✭


    Hi all,

    I got a new gas boiler installed recently with a hive thermostat that is able to boost the hot water via a motorized valve, the issue is when I boost the hot water some of the rads loose temperature is it normal?


Comments

  • Hosted Moderators Posts: 3,496 ✭✭✭DGOBS


    What boiler is it?


  • Registered Users, Registered Users 2 Posts: 3,097 ✭✭✭stevek93


    ideal logic 18kw condensing boiler


  • Hosted Moderators Posts: 3,496 ✭✭✭DGOBS


    ok, shouldn't really have a dramatic effectualness the boiler is close to undersized.

    One thing to check, it the balance valve on the hot water cylinder open too far (this would in essence rob the CH when the hot water is on)