Vokera mynute 16e pressure problem

Options
  • 01-12-2019 6:58pm
    #1
    Registered Users Posts: 5


    My vokera mynute 16e pressure is dangerously low,I looked up manuals and mine is semi sealed system, there is meant to be a filling loop ,I've checked under the boiler and in the hotpress and can not find it , I am freezing any help would be gratefully appreciated, I can show pics of hotpress if that would help


Comments

  • Registered Users Posts: 78 ✭✭scudodave


    My Vokera has a filling stopcock in the hot press near the pressure vessel,when you turn it you hear the pressure vessel filing.
    Try to post a photo, someone on hear will help.
    Best of luck.


  • Registered Users Posts: 5 Tattoo39


    Would mine be the same as yours????can you upload pics on here ,can't seem to see how you can


  • Hosted Moderators Posts: 3,496 ✭✭✭DGOBS


    Low water pressure isn't dangerous, your boiler has a low water pressure switch and will not operate is the water pressure is too low.

    If your system is 'semi-sealed' then your water pressure will only be roughly 0.1 bar for ever storey above your boiler the filling tank is.
    (i.i if your in a two storey house you would expect about 0.2 bar) and it does not require refilling.

    Just on this particular boiler, if it's not working, and you believe it is a low water pressure issue, to check:
    reset the boiler making sure the timer is calling for heat, and listen carefully, if all you here a single click from behind the front panel and the boiler does absolutely nothing else, then yes, you have a low water pressure problem. (the click is the PCB relay when there is a water pressure issue)


  • Registered Users Posts: 5 Tattoo39


    It's working now on 0.2 ,is that not very low for the presser gauge to be at on the boiler,some forums I'm reading say it should be between 1 and 1.5,I'm just afraid if it keeps dropping that my boiler will completely knock out ,that's the last thing I need coming up to Christmas as I was only recently made redundant


  • Registered Users Posts: 9,931 ✭✭✭dodzy


    Tattoo39 wrote: »
    It's working now on 0.2 ,is that not very low for the presser gauge to be at on the boiler,some forums I'm reading say it should be between 1 and 1.5,I'm just afraid if it keeps dropping that my boiler will completely knock out ,that's the last thing I need coming up to Christmas as I was only recently made redundant

    The pressure gauge will typically rise as the water heats (and expands) increasing the reading slightly. Boilers typically need a lot less than 1bar to operate. You won’t get 1 bar of static pressure in a normal house anyway, unless the filling loop is tapped into the main supply as the height differential of the cold water tank in attic is not sufficient.


  • Advertisement
  • Hosted Moderators Posts: 3,496 ✭✭✭DGOBS


    0.2 bars is fine for this boiler, as it has a low water pressure switch as said above. (normal for a semi-sealed system)
    1-1.5 bar would be on a fully sealed system.


  • Registered Users Posts: 5 Tattoo39


    Thanks very much for all the replies ,It has put my mind at ease a bit ,it is working now and i am going to keep an eye on it ,i just thought 0.2 was low from what other forums had stated but all seems ok