Ochsner O Tronic Classic - advice needed?

  • 31-10-2019 12:32am
    #1
    Registered Users Posts: 65 ✭✭✭ Civil Eng


    Evening all,

    I’ve recently bought a house that has a Ochsner O Tronic Heat Pump for heating. I’m having quite a bit of difficulty at the minute understanding how best to use it but also I’m quite concerned at the energy consumption of the heat pump. I estimate that it’s consuming power at 4kW when it’s running.

    Is that normal consumption?

    Any advice on how best to use this system?


Comments

  • Registered Users Posts: 10,927 ✭✭✭✭ Calahonda52


    What size is the house?
    floor are being heated/HW consumption

    have u a night rate meter?
    Have u a buffer tank?

    Lets assume the HP has COP of 4 or even 5
    That means that the heat output at 4kW in is about 16 or 20 kW.

    My gas fired house boiler is 28 kW
    so we need more detail


  • Registered Users Posts: 65 ✭✭✭ Civil Eng


    What size is the house? 3000sqm
    floor are being heated/HW consumption - Floors only

    have u a night rate meter? Yes
    Have u a buffer tank? What’s this?

    Lets assume the HP has COP of 4 or even 5
    That means that the heat output at 4kW in is about 16 or 20 kW.

    My gas fired house boiler is 28 kW
    so we need more detail

    Answers above