stove keeps dumping water into header tank

  • 29-09-2018 10:10pm
    #1
    Registered Users, Registered Users 2 Posts: 8


    I have had a stove with back boiler fitted in too a bungalow the Plummer ran the pipe work up onto the crawl space and back down into the hotpress I think the distance was about 45 too 50ft from stove too tank Plummer said it would work as a gravity flow

    curalation pump is fitted on the flow pipe in hotpress near tank the problem I'm.having is when I light the stove once it heats up the stat turns on the pump and the rad get Luke warm ish but the stove dumps the hot water into the header tank the flow pipe does be red hot and the return pipe is always cold

    any advice would be appreciated on this as Plummer isn't bother about coming back


Comments

  • Registered Users, Registered Users 2 Posts: 464 ✭✭2forjoy


    Could be a valve closed


  • Registered Users, Registered Users 2 Posts: 3,991 ✭✭✭jimf


    so many things don't sound right to me

    the plumbing lads will be on later and will be able to advise

    if im reading your post correctly 45FT for a gravity circuit seems way too long

    there should be no valves etc on this circuit and all should be done in 1" copper

    leave it off for now solid fuel is not something to be messed with

    also where is the stat to turn on the pump situated


  • Registered Users, Registered Users 2 Posts: 8 walsh2518


    jimf wrote: »
    so many things don't sound right to me

    the plumbing lads will be on later and will be able to advise

    if im reading your post correctly 45FT for a gravity circuit seems way too long

    there should be no valves etc on this circuit and all should be done in 1" copper

    leave it off for now solid fuel is not something to be messed with

    also where is the stat to turn on the pump situated

    hi jimf

    the stat was in the hotpress but I had an electrician move it too the flow pipe at the back of the stove
    when he was looking at it he did say there was no bypass or heat leak rad i think he call it put so he was gping too wire a zones too open when the pump would turn on


  • Registered Users, Registered Users 2 Posts: 3,991 ✭✭✭jimf


    the most important thing with a back boiler is a proper working gravity circuit

    for the very reason if you have a power out with the stove lighting the water has to be able to get away from the stove without the assistance of the pump


  • Registered Users, Registered Users 2 Posts: 1,135 ✭✭✭Redriddick


    walsh2518 wrote:
    the stat was in the hotpress but I had an electrician move it too the flow pipe at the back of the stove when he was looking at it he did say there was no bypass or heat leak rad i think he call it put so he was gping too wire a zones too open when the pump would turn on


    Do not put a valve or zone on the flow or return, if you do you literally have a bomb in your house.


  • Advertisement
  • Registered Users, Registered Users 2 Posts: 8 walsh2518


    Redriddick wrote: »
    Do not put a valve or zone on the flow or return, if you do you literally have a bomb in your house.

    that the last thing i like too hear this was done by a recommended Plummer that's been plumming with 40yrs

    as far as I know there isn't any valve or zone on the flow or return the way the electrician explain it too me was there was no bypass too a rad fitted so when I lite the stove the hot water was only going too the tank unless I manually open a zone or turned on one of the zones at the clock
    so for safety sake he wire a zone too open automatically when the stat turns on the circulation pump


  • Registered Users, Registered Users 2 Posts: 3,991 ✭✭✭jimf


    walsh2518 wrote: »
    that the last thing i like too hear this was done by a recommended Plummer that's been plumming with 40yrs

    as far as I know there isn't any valve or zone on the flow or return the way the electrician explain it too me was there was no bypass too a rad fitted so when I lite the stove the hot water was only going too the tank unless I manually open a zone or turned on one of the zones at the clock
    so for safety sake he wire a zone too open automatically when the stat turns on the circulation pump

    im afraid you need to have this whole install checked over before using it again
    there should be no switches valves or otherwise need to be turned on when you light the stove

    we know its not what you want to hear but its the only advice we can give you


  • Registered Users, Registered Users 2 Posts: 8 walsh2518


    jimf wrote: »
    im afraid you need to have this whole install checked over before using it again
    there should be no switches valves or otherwise need to be turned on when you light the stove

    we know its not what you want to hear but its the only advice we can give you

    thanks for the advice i was guessing i would have too get someone new too look it over and see what can be done

    I don't know much about plumming but just a question what would your thoughts be about installing a heat genie systemlink would it improve things it's was just a suggestion from a friend


  • Registered Users, Registered Users 2 Posts: 3,991 ✭✭✭jimf


    it will not help you in any way with the issue you have


    post your area one of the lads on here may be able to help or suggest somebody in your area


  • Registered Users, Registered Users 2 Posts: 8 walsh2518


    jimf wrote: »
    it will not help you in any way with the issue you have


    post your area one of the lads on here may be able to help or suggest somebody in your area

    thanks for the advice

    area is cork/limerick nearest places would be kanturk/Newcastlewest


  • Advertisement
  • Registered Users, Registered Users 2 Posts: 21,810 ✭✭✭✭Water John


    One must wonder is the vent not on the highest point of the line and thus is the pipe airlocking?