16mm2 v 25mm2 tails

  • 31-08-2018 9:16am
    #1
    Registered Users, Registered Users 2 Posts: 22


    Hi all,
    For a medium size house with a heat pump, the MIC calculation allowing for diversity is at the limit for 16mm PVC insulated cable. Are 25mm2 tails being used in domestic installations with heat pumps / other than cost and workability, what are the main disadvantages using 25mm2 in place of 16mm2?
    Thank you,


Comments

  • Moderators, Home & Garden Moderators, Technology & Internet Moderators, Regional East Moderators Posts: 12,641 Mod ✭✭✭✭2011


    No disadvantage at all. I wired a few in 25 sq back in the day.
    The larger cable reduces volt drop and earth fault loop impedance.