Attic Insulation options

  • 03-08-2018 4:06pm
    #1
    Registered Users, Registered Users 2 Posts: 215 ✭✭


    Hi,
    Doing a new build (bungalow) and we are just getting ready for slabbing the roof, before we close up i want to slip up the obs boards for flooring the attic for storage. So my BER calls for 2 layers of 150mm of mineral wool laid in opposite directions to achieve the value of 0.15 W/m2K. My BER Engineer has said if i want to remove one of the layers of mineral wool that i would need to do a 82.5mm Xtratherm Thin R insulated board(70mm insulation + 12.5 mm plasterboard) on the underside to make up for the 150mm. They are very costly and im looking for other options. If i raise the floor i will have to bend down for every more, and i want the full space for storage. Just looking to see what my options are if any
    Thanks


Comments

  • Subscribers Posts: 42,581 ✭✭✭✭sydthebeat


    32.5mm insulated plasterboard on ceiling
    150 quilt between joists
    50 PIR on Joists under flooring.

    Ergo you only loose 50mm of headroom


  • Registered Users, Registered Users 2 Posts: 1,997 ✭✭✭The_Bullman


    I'm in a similar dilemma.

    Is there a website(or table/chart) for comparing different insulation types and thicknesses that you could recommend.


  • Registered Users, Registered Users 2 Posts: 13,155 ✭✭✭✭Calahonda52


    covey09 wrote: »
    Hi,
    Doing a new build (bungalow) and we are just getting ready for slabbing the roof, before we close up i want to slip up the obs boards for flooring the attic for storage. So my BER calls for 2 layers of 150mm of mineral wool laid in opposite directions to achieve the value of 0.15 W/m2K. My BER Engineer has said if i want to remove one of the layers of mineral wool that i would need to do a 82.5mm Xtratherm Thin R insulated board(70mm insulation + 12.5 mm plasterboard) on the underside to make up for the 150mm. They are very costly and im looking for other options. If i raise the floor i will have to bend down for every more, and i want the full space for storage. Just looking to see what my options are if any
    Thanks

    What depth are the ceiling joists?
    What material is under the slates/tiles?

    “I can’t pay my staff or mortgage with instagram likes”.



  • Registered Users, Registered Users 2 Posts: 215 ✭✭covey09


    The Joists are 220mm the roof is felted and slated


  • Moderators, Home & Garden Moderators Posts: 10,146 Mod ✭✭✭✭BryanF


    Is it cross (double) battened outside the breathable felt?


  • Advertisement
  • Registered Users, Registered Users 2 Posts: 13,155 ✭✭✭✭Calahonda52


    covey09 wrote: »
    The Joists are 220mm the roof is felted and slated

    so the ceiling joists are 220 and your BER-head wants you to lay 150 between and 150 across.
    This is a careless design, as the across layer will undulate across the joists like the bog roads around Ferbane, leaving an air passage underneath for wind from the ventilated eaves to pass under the second layer and largely negate the value of all the insulation.
    The across layer will only go as far as the intersection of ceiling joist and roof rafter, leaving maybe 10 inches of the ceiling/wall/wallplate with only one layer.

    As I said, careless.

    Is the felt breathable to address BryanF's question

    “I can’t pay my staff or mortgage with instagram likes”.



  • Registered Users, Registered Users 2 Posts: 31,232 ✭✭✭✭Lumen


    Loose fill cellulose?


  • Registered Users, Registered Users 2 Posts: 13,155 ✭✭✭✭Calahonda52


    Lumen wrote: »
    Loose fill cellulose?

    depending on the full eave/soffit/facia/roof detail, cellulose will work only with properly fitted ventilation baffles

    “I can’t pay my staff or mortgage with instagram likes”.



  • Registered Users, Registered Users 2 Posts: 215 ✭✭covey09


    so the ceiling joists are 220 and your BER-head wants you to lay 150 between and 150 across.
    This is a careless design, as the across layer will undulate across the joists like the bog roads around Ferbane, leaving an air passage underneath for wind from the ventilated eaves to pass under the second layer and largely negate the value of all the insulation.
    The across layer will only go as far as the intersection of ceiling joist and roof rafter, leaving maybe 10 inches of the ceiling/wall/wallplate with only one layer.

    As I said, careless.

    Is the felt breathable to address BryanF's question

    Thanks your very helpful.


  • Registered Users, Registered Users 2 Posts: 72 ✭✭Vote4Napoleon


    I went with 8" metac between 9" joists and then slabbed with 50mm pir