replace triton t90i

Options
  • 13-07-2018 11:21am
    #1
    Registered Users Posts: 693 ✭✭✭


    hello im wondering what should i replace my triton t90i with id like to stay with the Triton brand and something around the same size if possible


Comments

  • Registered Users Posts: 16,928 ✭✭✭✭Sleeper12


    Triton t90sr is de the way forward

    As your shower is so old your electrician might need to upgrade the fuse at the fusebox. You need a 40amp rcbo. Yours might be 32amp

    There is a test button on the rcbo. This should be tested every 3 months.


  • Registered Users Posts: 693 ✭✭✭Conchurl


    Sleeper12 wrote: »
    Triton t90sr is de the way forward

    As your shower is so old your electrician might need to upgrade the fuse at the fusebox. You need a 40amp rcbo. Yours might be 32amp

    There is a test button on the rcbo. This should be tested every 3 months.

    Is it a straight swap of the showers or is there more to it?


  • Registered Users Posts: 16,928 ✭✭✭✭Sleeper12


    Conchurl wrote:
    Is it a straight swap of the showers or is there more to it?

    That depends on your cable size and the rcbo. If cable & rcbo are good then it is a straight swap


  • Registered Users Posts: 693 ✭✭✭Conchurl


    Sleeper12 wrote: »
    That depends on your cable size and the rcbo. If cable & rcbo are good then it is a straight swap

    the cable is 10mm comming into my old shower but the trip switch says C 32


  • Registered Users Posts: 693 ✭✭✭Conchurl


    Here is a pic


  • Advertisement
  • Registered Users Posts: 16,928 ✭✭✭✭Sleeper12


    Cable size is perfect. The 32 amp fuse is undersized for a 9kw shower. It's better to change it for a 40amp rcbo as it might trip randomly


  • Registered Users Posts: 693 ✭✭✭Conchurl


    Sleeper12 wrote: »
    Cable size is perfect. The 32 amp fuse is undersized for a 9kw shower. It's better to change it for a 40amp rcbo as it might trip randomly

    would that be a big job for an electrician or does he just swap out the 32 for a 40?


  • Registered Users Posts: 16,928 ✭✭✭✭Sleeper12


    Conchurl wrote:
    would that be a big job for an electrician or does he just swap out the 32 for a 40?


    Usually a 20/30 minute job including issuing the cert