13 or 20 amp for dishwasher and washing machine

  • 19-06-2018 6:37am
    #1
    Registered Users, Registered Users 2 Posts: 340 ✭✭


    greetings. we are getting a kitchen upgrade which will have new intergrated washing machine and dishwasher. at the moment they are both plugged into a single socket with a double adapter. this single socket will be changed to a double socket but because the units will be intergrated i was thinking of adding an isolator switch. my question is is it best to have a 20amp fuse or 13amp both machines have been used at the same time and we never had any issues previously.


Comments

  • Moderators, Home & Garden Moderators, Technology & Internet Moderators, Regional East Moderators Posts: 12,641 Mod ✭✭✭✭2011


    lookitsme wrote: »
    at the moment they are both plugged into a single socket with a double adapter. this single socket will be changed to a double socket

    Getting rid of the adapter is a very good idea.
    i was thinking of adding an isolator switch. my question is is it best to have a 20amp fuse or 13amp both machines have been used at the same time and we never had any issues previously.

    First off my understanding is that each appliance should have a dedicated isolator. However I am not fully up to speed with all of the domestic regulations as I only work in the industrial sector so I will let someone for familiar with this advise you.

    Secondly, the plugs for the appliances will contain a fuse, so there is no benefit with installing another fuse in series with this. So for isolation install an unfused isolator. Typically a 20A double pole isolator would be used.


  • Registered Users, Registered Users 2 Posts: 2,567 ✭✭✭Risteard81


    Not just getting rid of the double adaptor - two single socket outlets would be a superior arrangement to one double socket outlet as a double socket outlet only has a maximum current rating of 20A and not 2 * 13A as many might assume. Ideally they would be two separate circuits.


  • Registered Users, Registered Users 2 Posts: 470 ✭✭17larsson


    One 20A double pole switch (as long as the circuit is a radial and on a 20A MCB) can be used for two sockets a long as it is labeled correctly