    Good morning,
    Last night i went to put the heating on as it got a bit chilly.
    I hit boost on the Hive system and nothing started on the boiler but it was ok during the week as was useing it to heat hot water. The gauge is reading 1.5 bar so i pressed the Reset button on the front of the boiler, i assume it goes through its own checks then i hit boost and nothing from the boiler. Any ideas what it could be? Its only a new boiler fitted last April.


Comments

  • Hosted Moderators Posts: 3,496 ✭✭✭DGOBS


    Any warning lights/numbers on the boiler?
    Also, on Hive Receiver was the central heating button solid green or flashing green? (not the top power light)


  • Registered Users Posts: 1,019 ✭✭✭anthonyos


    what number or letter is on the boiler display


  • Registered Users Posts: 1,660 ✭✭✭Payton


    Sorry i should have posted it there is 00 on the display. The central heating on the reciever is a solid green.


  • Hosted Moderators Posts: 3,496 ✭✭✭DGOBS


    0 on the display means boiler is waiting for a 'call for heat' , solid green on the Hive receiver is a 'call for heat'

    Is you Hive dual zone (separate heat/hot water) if so, what happens when you call for hot water?

    Was Hive installed with the boiler, or as an add on? and if so did the installer remove to old room thermostat (if you had one) and if it is still there, is it turned up fully


  • Registered Users Posts: 1,660 ✭✭✭Payton


    DGOBS wrote: »
    0 on the display means boiler is waiting for a 'call for heat' , solid green on the Hive receiver is a 'call for heat'

    Is you Hive dual zone (separate heat/hot water) if so, what happens when you call for hot water?

    Was Hive installed with the boiler, or as an add on? and if so did the installer remove to old room thermostat (if you had one) and if it is still there, is it turned up fully

    Its dual system HW and Heating. It was an add on.
    A week or so ago i asked was it ok to remove the EPH thermostat from the hall and i was told i can so the wires for the thermostat are on a connector block behind that is tapped up and i have the Hive in that location now.


  • Advertisement
  • Hosted Moderators Posts: 3,496 ✭✭✭DGOBS


    aha, the NO and Common wires from that thermostat need to be joined together, there's your problem.


  • Registered Users Posts: 1,660 ✭✭✭Payton


    All good now. Cheers.
    The pressure gauge is hitting the 2 mark, is that an issue?


  • Hosted Moderators Posts: 3,496 ✭✭✭DGOBS


    2 is ok when under full load hot, if your getting over 2.5 you may have an expansion issue developing