Hi there,
There is an issue with role permissions that is being worked on at the moment.
If you are having trouble with access or permissions on regional forums please post here to get access: https://www.boards.ie/discussion/2058365403/you-do-not-have-permission-for-that#latest

Stanley stove with ecoflam burner problem

  • 24-11-2017 11:12pm
    #1
    Registered Users, Registered Users 2 Posts: 2


    Hi all, I'm totally new here and am hoping I can get some help with a burner issue I have. The burner goes through pre-purger and lights but flame goes out after say 6-7seconds. I have fitted a new solenoid, photocell and control box but still does the same. I'm at the end of my ideas as to what this could be. Please help!


Comments

  • Registered Users, Registered Users 2 Posts: 800 ✭✭✭esox28


    silly question but have you done the basics change jet, replaced burner hose, cleaned or replaced pump filter and tank filter, checked your fire valves operation confirmed oil pressure and vacuum on pump. cleaned air box?


  • Registered Users, Registered Users 2 Posts: 2 tee7x7


    Well after some time with trying everything I eventually found that the nozzle had been changed for the incorrect spray pattern and the photocell wouldn't pick up correctly. Changed nozzle and all working great. Thanx for your time esox :)