    Hi folks

    How many carbon monoxide alarms are required in a bog standard 4 bed semi detached house? There is a gas boiler located in a small utility room just off the kitchen towards the rear of the house and there is also a gas fire place in the front sitting room. Would one alarm located mid way (approx. 5 metres from the entrance to both rooms) between the two rooms in the hall be sufficient? Upstairs there is just a bog standard hotpress.

    Thanks!


Comments

  • Registered Users, Registered Users 2 Posts: 78,610 ✭✭✭✭Victor


    There may be different rules for different types of properties.

    Is it rented out?

    Is it a new build?


  • Registered Users, Registered Users 2 Posts: 762 ✭✭✭PGL


    Victor wrote: »
    There may be different rules for different types of properties.

    Is it rented out?

    Is it a new build?

    Hi Victor. I own and live in the property which is roughly 15 to 20 years old.


  • Moderators, Society & Culture Moderators Posts: 40,800 Mod ✭✭✭✭Gumbo


    PGL wrote: »
    Hi Victor. I own and live in the property which is roughly 15 to 20 years old.

    Technically speaking none are required.
    But under the current building regulations, if your house was built tomorrow, Building Control would enforce the following :

    CO Alarm in the room with the gas boiler
    CO alarm in the room with the fireplace
    CO alarm in the room above if the chimney passes through it.
    CO alarm on the first floor landing (within 5m of the entrance to the rooms)


  • Registered Users, Registered Users 2 Posts: 762 ✭✭✭PGL


    Thanks for the feedback. Regardless of the fact it's not a new build, I'm going to install one of these alarms for peace of mind. My question is whether one alarm could be placed in the hallway, half way between the gas boiler and the fireplace?


  • Registered Users, Registered Users 2 Posts: 606 ✭✭✭famagusta


    No put them in as the poster above said, he is spot on. They are not that expensive anyway


  • Advertisement
  • Moderators, Society & Culture Moderators Posts: 40,800 Mod ✭✭✭✭Gumbo


    PGL wrote: »
    Thanks for the feedback. Regardless of the fact it's not a new build, I'm going to install one of these alarms for peace of mind. My question is whether one alarm could be placed in the hallway, half way between the gas boiler and the fireplace?

    No. Because if someone is asleep in the sitting room, by the time the alarm in the hall goes off, they are dead.

    If someone is asleep in the bedroom where the flue passes through, by the time the alarm goes off they are dead. See what I mean.

    At the very least, you should have one in each room that the heat producing appliance is located.


  • Registered Users, Registered Users 2 Posts: 4,825 ✭✭✭LirW


    Basically everywhere where you have the heat source (fireplace, solid fuel stove), boiler and the chimney passing through. I'd be more inclined getting too many than risking my family's life.
    If you have the chimney passing through between 2 bedrooms put one in each. If you have an attic conversion with the chimney passing through, put an alarm in.
    CO is no joke.


  • Registered Users, Registered Users 2 Posts: 762 ✭✭✭PGL


    Thanks for all the feedback folks. I'd already bought 1. I'll now pick up 2 more, and install one in front sitting room, one in utility and one on the first floor landing.