Advertisement
If you have a new account but are having problems posting or verifying your account, please email us on hello@boards.ie for help. Thanks :)
Hello all! Please ensure that you are posting a new thread or question in the appropriate forum. The Feedback forum is overwhelmed with questions that are having to be moved elsewhere. If you need help to verify your account contact hello@boards.ie
Hi there,
There is an issue with role permissions that is being worked on at the moment.
If you are having trouble with access or permissions on regional forums please post here to get access: https://www.boards.ie/discussion/2058365403/you-do-not-have-permission-for-that#latest

Solar set up for camping

  • 15-06-2017 3:11pm
    #1
    Registered Users, Registered Users 2 Posts: 1,370 ✭✭✭


    Hi all, struggling a bit with this, to set up for camping,

    how does this look

    Solar Panel

    4mm2 cable, 5M, do i need 8mm2?

    circuit breaker

    1 circuit breaker with a 15 Amp fuse between pv and controller,

    controller

    4mm2 cable, <1M, do i need 8mm2?

    1 circuit breaker with a 25 Amp fuse between battery and controller,

    115a Halfords Leisure battery
    **

    Out of the load connectors on the controller

    4mm2 cable, <1M, do i need 8mm2?

    1 circuit breaker with a 25 Amp fuse between controller and switch panel,

    Switch Panel

    Have those 4 switches controlling my fridge (4A when on), 12v socket (maha c9000 battery charger at home, possibly a 150w inverter at times) usb sockets, lights (a few amps)

    Thanks for any comments


Comments

  • Posts: 5,238 ✭✭✭ [Deleted User]


    eeepaulo wrote: »

    how does this look

    Solar Panel

    4mm2 cable, 5M, do i need 8mm2?


    It'd be cheaper to buy and more practical day to day if it was a permanent fixture.

    4mm² is fine up to about 150W @ 18V
    eeepaulo wrote: »

    Fine
    I like breakers, fuses are cheaper.

    eeepaulo wrote: »
    1 circuit breaker with a 15 Amp fuse between pv and controller,

    Not necessary, it'll never trip. You need a switch-disconnect here to isolated the PV input before cutting power to the solar controller for any reason.
    eeepaulo wrote: »
    controller
    4mm2 cable, <1M, do i need 8mm2?

    That's exactly what I wanted before they developed it. Double your battery life expectancy with that nugget.

    ≥6mm²
    eeepaulo wrote: »
    1 circuit breaker with a 25 Amp fuse between battery and controller,
    12A/13A fuse for a 10A controller or 40A for 6mm² cable

    eeepaulo wrote: »
    Out of the load connectors on the controller

    4mm2 cable, <1M, do i need 8mm2?

    4mm² for 10 amp is adequate.

    eeepaulo wrote: »
    1 circuit breaker with a 25 Amp fuse between controller and switch panel,

    12A fuse for 10A Load Controller

    eeepaulo wrote: »

    Have those 4 switches controlling my fridge (4A when on), 12v socket (maha c9000 battery charger at home, possibly a 150w inverter at times) usb sockets, lights (a few amps)

    Don't run the fridge or inverter off the load control terminals. Pretty sure it'll say as much in the manual. They're too heavy for the wee controller.

    Delete the cig. lighter plug from your inverter, install an inline fuse and hard-wire it to the battery or bus bar.

    USB Sockets, 12V Sockets, Lights no probs. Don't exceed 120W total load or buy a larger controller or wire loads from distribution. The Load terminals are for low/high voltage protected appliances (the stuff you are likely to forget about and drains the battery).


  • Registered Users, Registered Users 2 Posts: 1,370 ✭✭✭eeepaulo


    I'm reading more.....

    Just a quick question though, should I buy the 20a or 30a controller, based on my need?


  • Posts: 5,238 ✭✭✭ [Deleted User]


    10A Solar controller : 150Wp solar flat-mounted / 120W Optimised.
    10A Load controller: Max controlled Load 120W.

    20A Solar controller : 300Wp solar flat-mounted / 240W Optimised.
    20A Load controller: Max controlled Load 240W.

    30A Solar controller : 450Wp solar flat-mounted / 360W Optimised.
    30A Load controller: Max controlled Load 360W.

    {x2 for 24v}

    No load controller likes fridges or inverters. You can coerce them into triggering relays that load control fridges and inverters though.


Advertisement