SOREL STD 3 Setup

  • 18-05-2017 9:17am
    #1
    Registered Users, Registered Users 2 Posts: 700 ✭✭✭


    Hi is anyone familiar with this Controller? Plumber change the Circulation pump and Now I see a different view on this controller?

    Is it easy to change back ?

    The image2 is the original with one Solar panel and S1 S2 S3 and S3 being the HW tank

    The New Display has 2 Panels ??

    and S2 = Tank???

    Regards

    Gary


Comments

  • Registered Users, Registered Users 2 Posts: 1,422 ✭✭✭dathi


    scroll down to 8.1 menu lock and unlock it if its locked with the + or - buttons then go back to main menu and scroll down to 7 special functions press ok to enter and then scroll to 7.12 sol and thermostat press select and then reset the menu lock
    pm sent


  • Registered Users, Registered Users 2 Posts: 700 ✭✭✭garyh3


    Thanks for that I did that but the S3 Dump pump came on and the S3 temp started to Drop it was only at 50 ? so I put it back to the other diagram and it stopped the dump pump.

    Do the the Settings need to be tweeked?

    Gary

    Pics added or settings

    That Offset looks high?


  • Registered Users, Registered Users 2 Posts: 700 ✭✭✭garyh3


    Last pic