Window Restrictors as opposed to Guarding?

  • 28-02-2017 2:08pm
    #1
    Registered Users, Registered Users 2 Posts: 907 ✭✭✭


    Is it adequate to install window restrictors instead of guards on first floor window openings with a cill height between 300-800 above the floor level?

    my guess is no because it would mean that the window couldn't be used as a means of escape but just wanted to double check. I've seen the guards on a few new houses lately and they are awful.


Comments

  • Registered Users, Registered Users 2 Posts: 3,725 ✭✭✭Metric Tensor


    AFAIK - There are window restrictors that you can use that have a little pinch or press down action that allow the windows to be used as fire escape windows.

    However, I don't think this is a substitute for guarding. Moreso this is an additional safety item for the window (that is above 800) for child safety.

    That's my view - I think kceire's might hold more weight!


  • Registered Users, Registered Users 2 Posts: 907 ✭✭✭bemak


    AFAIK - There are window restrictors that you can use that have a little pinch or press down action that allow the windows to be used as fire escape windows.

    However, I don't think this is a substitute for guarding. Moreso this is an additional safety item for the window (that is above 800) for child safety.

    That's my view - I think kceire's might hold more weight!


    Ya I was aware of those restrictors as well. Best solution is probably to put a fixed section of glazing from cill to 800mm above floor level with an openable section above.


  • Moderators, Society & Culture Moderators Posts: 40,340 Mod ✭✭✭✭Gumbo


    bemak wrote: »
    Is it adequate to install window restrictors instead of guards on first floor window openings with a cill height between 300-800 above the floor level?

    my guess is no because it would mean that the window couldn't be used as a means of escape but just wanted to double check. I've seen the guards on a few new houses lately and they are awful.

    The window restrictor is a different requirement to guarding.
    The restrictor is required in all first floor windows and I insist on them been installed even in bathrooms etc. It's there to stop a child opening a window and going for a drop which we have seen quite a few times recently (phibsboroigh and cork).

    The guard is there as part of TGD K rather than B above.
    If the door can fully open, the guard is required also, toughened glass below the 800mm mark.


  • Registered Users, Registered Users 2 Posts: 907 ✭✭✭bemak


    this is what i was looking to do.

    does the 400mm cill create another problem? i.e. something to step up on? hence the restrictor


  • Moderators, Society & Culture Moderators Posts: 40,340 Mod ✭✭✭✭Gumbo


    bemak wrote: »
    this is what i was looking to do.

    does the 400mm cill create another problem? i.e. something to step up on? hence the restrictor

    The opening section requires a restrictor either way.
    The step up onto the cill has to be seen. In some cases I've requested the guarding at 800 above the cill height if it's deep enough to stand in.


  • Advertisement
  • Registered Users, Registered Users 2 Posts: 326 ✭✭fatty pang


    kceire wrote: »
    The window restrictor is a different requirement to guarding.
    Indeed and it wouldn’t function as a permanent barrier.
    The restrictor is required in all first floor windows and I insist on them been installed even in bathrooms etc. .
    TGD-B (1.5.6e) doesn’t explicitly distinguish between windows at ground floor and above when it comes to requiring restrictors.:confused:
    The guard is there as part of TGD K rather than B above.
    If the door can fully open, the guard is required also, toughened glass below the 800mm mark.
    Fully opened is incorrect. Guarding must prevent a 100mm diameter sphere from passing through any opening or gap. The ‘safety’ glass must be of adequate strength.


  • Registered Users, Registered Users 2 Posts: 326 ✭✭fatty pang


    bemak wrote: »
    this is what i was looking to do.

    does the 400mm cill create another problem? i.e. something to step up on? hence the restrictor

    NHBC provide clear guidance on the issues involved here -
    www.nhbc.co.uk/Builders/ProductsandServices/.../filedownload,40525,en.pdf
    You will also need to address the issue of the large fixed light if height differential is >600 between floor level and outside ground level. The glazing will have to withstand specified loads in the absence of any other barrier. Loads described in EN 1991-1-1 are more onerous then BS 6180. I will leave it to those with competence to adjudge which is appropriate.


  • Registered Users, Registered Users 2 Posts: 907 ✭✭✭bemak


    What's the title of that document if you don't mind me asking. Link is down


  • Registered Users, Registered Users 2 Posts: 326 ✭✭fatty pang


    bemak wrote: »
    What's the title of that document if you don't mind me asking. Link is down

    NHBC Technical Extra. Issue 17, Feb 2015. Its on their website.


  • Registered Users, Registered Users 2 Posts: 907 ✭✭✭bemak


    Got it. Thanks a mil. Great resource, never heard it it before!


  • Advertisement
  • Registered Users, Registered Users 2 Posts: 326 ✭✭fatty pang


    bemak wrote: »
    Got it. Thanks a mil. Great resource, never heard it it before!

    NHBC Standards - available for free - is what the Homebond manual ought to be. Then again NHBC is what Homebond ought to be.


  • Registered Users, Registered Users 2 Posts: 907 ✭✭✭bemak


    fatty pang wrote:
    NHBC Standards - available for free - is what the Homebond manual ought to be. Then again NHBC is what Homebond ought to be.

    I actually was considering buying the homebound manual but this is much better


  • Registered Users, Registered Users 2 Posts: 326 ✭✭fatty pang


    bemak wrote: »
    I actually was considering buying the homebound manual but this is much better

    I don't think they have updated it since the 7th Edition which had some archaic details when it was brand new. Joseph Litttle did a good appraisal of it in Construct Ireland at the time. I wouldn't hold out any hope of it ever coming close to the NHBC or even the Zurich manual.