Advertisement
If you have a new account but are having problems posting or verifying your account, please email us on hello@boards.ie for help. Thanks :)
Hello all! Please ensure that you are posting a new thread or question in the appropriate forum. The Feedback forum is overwhelmed with questions that are having to be moved elsewhere. If you need help to verify your account contact hello@boards.ie
Hi there,
There is an issue with role permissions that is being worked on at the moment.
If you are having trouble with access or permissions on regional forums please post here to get access: https://www.boards.ie/discussion/2058365403/you-do-not-have-permission-for-that#latest

Can I use UK consumer unit?

  • 31-10-2016 11:08am
    #1
    Registered Users, Registered Users 2 Posts: 17


    Got a few bargain buys in the UK before coming over to start our new build one being a consumer unit. I notice screwfix don't sell the same unit over here, does it not comply with Irish regulations? It is a split load, 100amp switch and 30amp RCD with 8 MCBs of various ampages and 2 RCBOs.
    Thanks for any replies


Comments

  • Registered Users, Registered Users 2 Posts: 10,952 ✭✭✭✭Stoner


    Most of the bits would be OK. Usually the main incomer here is say 80amps at the ESB side and fused down to 55 amps in the consumer units so 100 amp main incomer would need to be changed


  • Registered Users, Registered Users 2 Posts: 2,567 ✭✭✭Risteard81


    There are likely to be a number of other problems. The switch will be double pole rather than single pole, also it is not a switch fuse it is simply a switch disconnector. It will also be unsuitable for double pole RCBOs. I very much doubt that there would be any merit in trying to buy one and mod it to suit. It would make much more sense simply to purchase the correct unit in the first place.


  • Moderators, Home & Garden Moderators, Technology & Internet Moderators, Regional East Moderators Posts: 12,641 Mod ✭✭✭✭2011


    Offgridcoe wrote: »
    Got a few bargain buys in the UK before coming over to start our new build one being a consumer unit. I notice screwfix don't sell the same unit over here, does it not comply with Irish regulations? It is a split load, 100amp switch and 30amp RCD with 8 MCBs of various ampages and 2 RCBOs.
    Thanks for any replies


    Have you a link?


  • Registered Users, Registered Users 2 Posts: 15 Mrplod


    I would agree that there are some differences. One other thing to watch for is the RCD types. An AC type is still being used in the U.K. Where the A type is being used here. For all the savings it's probably not worth it


Advertisement