  • 16-10-2016 9:50pm
    #1
    Registered Users, Registered Users 2 Posts: 14,681 ✭✭✭✭


    Does anyone have a ball park figure for how much it would cost to replace a burnt out shower switch? The shower has stopped working on me and this seems to be the problem. I'd do it myself but frankly I haven't got a clue how to.


Comments

  • Registered Users, Registered Users 2 Posts: 22,584 ✭✭✭✭Steve


    Are you talking about a ceiling pull-cord switch?

    Not expensive but figuring out why it failed would be more important than replacing it.

    http://www.eurosales.ie/products/1298.html


  • Moderators, Home & Garden Moderators, Technology & Internet Moderators, Regional East Moderators Posts: 12,641 Mod ✭✭✭✭2011


    Steve wrote: »
    Are you talking about a ceiling pull-cord switch?

    Not expensive but figuring out why it failed would be more important than replacing it.

    http://www.eurosales.ie/products/1298.html

    These switches frequently fail. Assuming it is an instantaneous shower it is generally the largest single load in the installation. Many have low quality isolation switches which they switch off when not in use which can shorten the life of the unit considerably. Even more damaging is operating the switch under load conditions.

    I would recommend a high quality switch such as MK.


  • Registered Users, Registered Users 2 Posts: 14,681 ✭✭✭✭P_1


    Steve wrote: »
    Are you talking about a ceiling pull-cord switch?

    Not expensive but figuring out why it failed would be more important than replacing it.

    http://www.eurosales.ie/products/1298.html

    It's a switch on the wall outside the bathroom. I'm guessing the most expensive will be the call out and labour charge


  • Registered Users, Registered Users 2 Posts: 17,190 ✭✭✭✭Sleeper12


    P_1 wrote: »
    It's a switch on the wall outside the bathroom. I'm guessing the most expensive will be the call out and labour charge

    As "2011" says make sure you get a good quality switch. The very cheap ones can't handle the load. Personally I prefer to fit 50amp rather than 45amp when I can get them.
    As for your actual question on price. Best option is ring 2 or 3 electricians & ask for a quote over the phone. I would be expecting to pay €100 supplied & fitted give or take a little.


  • Registered Users, Registered Users 2 Posts: 10,952 ✭✭✭✭Stoner


    P_1 wrote:
    It's a switch on the wall outside the bathroom. I'm guessing the most expensive will be the call out and labour charge


    Switch on the wall is the only way to go imo.

    I use to use mk single gang units 45amp without issue.

    Pull cords are too much trouble imo.


  • Advertisement
  • Registered Users, Registered Users 2 Posts: 2,567 ✭✭✭Risteard81


    Stoner wrote: »

    Pull cords are too much trouble imo.
    I would certainly agree in relation to cheap pull cords, but good quality 50A pull cords such as the Crabtree or Click Polar offerings are actually very good and reliable.


  • Registered Users, Registered Users 2 Posts: 22,584 ✭✭✭✭Steve


    2011 wrote: »
    These switches frequently fail.
    Fail mechanically or electrically?

    I read 'burnt out' as an electrical fail as opposed to the string falling off :)


  • Moderators, Home & Garden Moderators, Technology & Internet Moderators, Regional East Moderators Posts: 12,641 Mod ✭✭✭✭2011


    Steve wrote: »
    Fail mechanically or electrically?

    I read 'burnt out' as an electrical fail as opposed to the string falling off :)

    Generally switches start to fail mechanically which leads to an electrical failure.

    The "burn out" formula = the square of the current by the resistance.

    or I^2 R, (watts)

    An instantaneous shower (which I assume this is) has a high current (a 9.5 kW shower draws around 40 amps). So if the contacts of the switch don't have to have a very high resistance to result in quite a bit of heat being generated.

    Mechanical wear can cause the resistance of the switch to increase. This can be exacerbated by operating the switch under land conditions. Frequent operation won't help either.


  • Registered Users, Registered Users 2 Posts: 22,584 ✭✭✭✭Steve


    I get all that, these switches would not normally be expected to open under load though. Which was why I asked was it more prone to mechanical failure.
    In fairness, even 45A resistive is not a big deal to break, inductive is a whole different story..


  • Moderators, Home & Garden Moderators, Technology & Internet Moderators, Regional East Moderators Posts: 12,641 Mod ✭✭✭✭2011


    Steve wrote: »
    I get all that, these switches would not normally be expected to open under load though. Which was why I asked was it more prone to mechanical failure.
    In fairness, even 45A resistive is not a big deal to break, inductive is a whole different story..

    This switch costs €6.84 + VAT.
    If you pay that little for a switch and you switch it on and off once a day for several years the chances of failure are high.
    When I worked as an electrician I replaced a lot of cheap shower switches like this.
    I can not recall replacing an MK or Crabtree equivalent. You get what you pay for.


  • Advertisement
  • Registered Users, Registered Users 2 Posts: 14,681 ✭✭✭✭P_1


    So out of interest how much would an MK or Crabtree switch set you back? Bearing in mind that I'm currently in a rental and the LL is unlikely to invest too much in the place.


  • Moderators, Home & Garden Moderators, Technology & Internet Moderators, Regional East Moderators Posts: 12,641 Mod ✭✭✭✭2011


    P_1 wrote: »
    So out of interest how much would an MK or Crabtree switch set you back? Bearing in mind that I'm currently in a rental and the LL is unlikely to invest too much in the place.

    In the UK they cost £10.31INC VAT


  • Registered Users, Registered Users 2 Posts: 22,584 ✭✭✭✭Steve


    2011 wrote: »
    This switch costs €6.84 + VAT.
    If you pay that little for a switch and you switch it on and off once a day for several years the chances of failure are high.
    When I worked as an electrician I replaced a lot of cheap shower switches like this.
    I can not recall replacing an MK or Crabtree equivalent. You get what you pay for.

    Not doubting you, just thinking with my engineer and devils advocate hat on as if I was asked to risk assess one.

    I don't know anyone who would operate the switch *every time* the shower is used. Would you not agree? I would say these are operated very infrequently?


  • Registered Users, Registered Users 2 Posts: 14,681 ✭✭✭✭P_1


    Steve wrote: »
    Not doubting you, just thinking with my engineer and devils advocate hat on as if I was asked to risk assess one.

    I don't know anyone who would operate the switch *every time* the shower is used. Would you not agree? I would say these are operated very infrequently?

    Do you mean turning it on before you use the shower and turning it off afterwards? I must be the exception then as that's what I was doing 90% of the time. I wonder if that's what broke it :o


  • Registered Users, Registered Users 2 Posts: 22,584 ✭✭✭✭Steve


    P_1 wrote: »
    So out of interest how much would an MK or Crabtree switch set you back? Bearing in mind that I'm currently in a rental and the LL is unlikely to invest too much in the place.

    Kellihers are MK agents for Ireland, can't find it on the website but if you call them they will quote you.

    http://www.kellihers.com/


  • Moderators, Home & Garden Moderators, Technology & Internet Moderators, Regional East Moderators Posts: 12,641 Mod ✭✭✭✭2011


    Steve wrote: »
    I don't know anyone who would operate the switch *every time* the shower is used.

    I do, my old man always does this. He insists that it is safer to switch it off when not in use. I think he is on his third switch now (no I'm not joking). Strange behavior (especially for an electrical engineer).

    Anecdotaly I would say that lot of older people do this sort of thing.

    Would you not agree? I would say these are operated very infrequently?

    In my house, yes.


  • Registered Users, Registered Users 2 Posts: 22,584 ✭✭✭✭Steve


    P_1 wrote: »
    Do you mean turning it on before you use the shower and turning it off afterwards? I must be the exception then as that's what I was doing 90% of the time. I wonder if that's what broke it :o

    It's very possible.

    I know the rigors that stuff like this has to go through to pass CE and be approved for use so am disappointed when I hear a tale such as yours. As you are renting, you can't go to the original installer and claim back.

    I guess that they bank on for the sake of less than €20 it's not worth the hassle.


  • Registered Users, Registered Users 2 Posts: 10,952 ✭✭✭✭Stoner


    Steve wrote:
    I don't know anyone who would operate the switch *every time* the shower is used. Would you not agree? I would say these are operated very infrequently?

    People do use them all the time though.

    This is an old can of worms tbh. It's going to get into the regs etc and go nowhere again imo

    For my part they are there for isolation to allow someone to work on the shower.

    But there is a counter argument.


  • Registered Users, Registered Users 2 Posts: 4,620 ✭✭✭enfant terrible


    Stoner wrote: »
    People do use them all the time though.

    This is an old can of worms tbh. It's going to get into the regs etc and go nowhere again imo

    For my part they are there for isolation to allow someone to work on the shower.

    But there is a counter argument.

    Should the switch be left on permanently.


  • Registered Users, Registered Users 2 Posts: 17,190 ✭✭✭✭Sleeper12


    Should the switch be left on permanently.

    Most if not all electricians say to leave it on. The pull cords in particular aren't designed to be turned on & off 4 or 5 times per day.
    Families have rows about this on a daily basis. What is clouding the issue even more is that all the latest electric showers have an led that is still on when shower is off. So now the homeowner is looking at 2 leds, one on shower & one on switch. To them they are wasting "Hundreds of euro per year". I'm sure this is a ploy from the manufactures to keep the switch turned off.

    Edit: Any possible savings on turning this tiny led off will be far outstripped by the cost of replacing the pull cord on a regular basis.


  • Advertisement
  • Registered Users, Registered Users 2 Posts: 4,620 ✭✭✭enfant terrible


    Sleeper12 wrote: »
    Most if not all electricians say to leave it on. The pull cords in particular aren't designed to be turned on & off 4 or 5 times per day.
    Families have rows about this on a daily basis. What is clouding the issue even more is that all the latest electric showers have an led that is still on when shower is off. So now the homeowner is looking at 2 leds, one on shower & one on switch. To them they are wasting "Hundreds of euro per year". I'm sure this is a ploy from the manufactures to keep the switch turned off.

    Edit: Any possible savings on turning this tiny led off will be far outstripped by the cost of replacing the pull cord on a regular basis.

    Thanks Sleeper,

    Would the shower then not be in stand by mode?

    We're always been told to plug out our tvs as stand by mode uses a lot of electricity apparently.


  • Registered Users, Registered Users 2 Posts: 17,190 ✭✭✭✭Sleeper12


    Thanks Sleeper,

    Would the shower then not be in stand by mode?

    We're always been told to plug out our tvs as stand by mode uses a lot of electricity apparently.

    I'm not an electrician so happy to be corrected here.

    Your DVD player Sky box etc, are still consuming electricity in standby mode. Up to 25% in some cases I think. The brains of the Sky Box is always on & always thinking. What day is it? do I need to record something today etc. This consumes power. But your electric shower is either on or off. Some showers do have pcb boards but the shower doesn't need to worry about timers or anything like that so off should mean off.
    I have seen faulty power rather than electric showers with the motor running when the power button is turned off though. Usually the pcb board is faulty.


  • Registered Users, Registered Users 2 Posts: 22,584 ✭✭✭✭Steve


    The lamps are generally neon on the switch and on the shower. They are used to indicate the presence of AC voltage.

    Typically they use about 1mA which by rough calculation would cost about €0.30 per year if left on 24/365.

    Think of the shower switch as a backup - similar to a cooker switch. It is a means of removing power when something goes wrong or for maintenance.


  • Moderators, Home & Garden Moderators, Technology & Internet Moderators, Regional East Moderators Posts: 12,641 Mod ✭✭✭✭2011


    Steve wrote: »
    The lamps are generally neon on the switch and on the shower. They are used to indicate the presence of AC voltage.

    Typically they use about 1mA which by rough calculation would cost about €0.30 per year if left on 24/365.

    You could alway disconnect the lamp and save a cool 30 cent :cool:


  • Registered Users, Registered Users 2 Posts: 22,584 ✭✭✭✭Steve


    2011 wrote: »
    You could alway disconnect the lamp and save a cool 30 cent :cool:

    Yeah but a REC would charge €100 for the call out... short wait of 300 years then profit!! :cool:

    (assuming you never have to replace the switch :D)


  • Registered Users, Registered Users 2 Posts: 4,620 ✭✭✭enfant terrible


    Steve wrote: »
    The lamps are generally neon on the switch and on the shower. They are used to indicate the presence of AC voltage.

    Typically they use about 1mA which by rough calculation would cost about €0.30 per year if left on 24/365.

    Think of the shower switch as a backup - similar to a cooker switch. It is a means of removing power when something goes wrong or for maintenance.

    The cooker switch on the wall should be left on too should it?


  • Registered Users, Registered Users 2 Posts: 14,681 ✭✭✭✭P_1


    Well the wiring on the back was a burnt mess but it's been fixed.


  • Closed Accounts Posts: 1,847 ✭✭✭Armchair Andy


    Does the proximity of the backing box (steel more so than dry lining) bear any difference to the lifetime of one of these switches? (Heat wise).
    I'm sure a 2 gang box on the vertical with a 2 gang switch would far outlive a single gang switch/ box.


  • Registered Users, Registered Users 2 Posts: 10,952 ✭✭✭✭Stoner


    Does the proximity of the backing box (steel more so than dry lining) bear any difference to the lifetime of one of these switches? (Heat wise). I'm sure a 2 gang box on the vertical with a 2 gang switch would far outlive a single gang switch/ box.


    It's more heat caused by poor connections rather than an inability for standard heat dissipation


  • Advertisement
  • Registered Users, Registered Users 2 Posts: 22,584 ✭✭✭✭Steve


    P_1 wrote: »
    Well the wiring on the back was a burnt mess but it's been fixed.

    That would worry me.

    It would suggest it's not a mechanical failure but a poor connection.

    Did you fix it yourself or get a sparks? I would have asked them to spot check various other connections around the house as the original guys who wired it may have been less than diligent.


  • Moderators, Home & Garden Moderators, Technology & Internet Moderators, Regional East Moderators Posts: 12,641 Mod ✭✭✭✭2011


    Steve wrote: »
    That would worry me.

    It would suggest it's not a mechanical failure but a poor connection.

    I have seen this quite a few times.
    When there is a high resistance on a cable with a large current flowing through it the heat can travel up the cable and cause the insulation to melt and blacken on the cable like this.


  • Registered Users, Registered Users 2 Posts: 22,584 ✭✭✭✭Steve


    2011 wrote: »
    I have seen this quite a few times.
    When there is a high resistance on a cable with a large current flowing through it the heat can travel up the cable and cause the insulation to melt and blacken on the cable like this.

    I've seen commercial switchrooms burn down because of issues like this, improperly tightened connects are lethal.

    In the one I saw, it was due to builders using a kango a few feet away digging a trench, the board wasn't checked after the works were completed and a 250A S/F went up.

    That's why I'd be worried and if it was my house, I's be going around checking all nearby connections. :)