Electrical help

  • 11-09-2016 10:02pm
    #1
    Registered Users, Registered Users 2 Posts: 89 ✭✭


    Is it ok to put 8 x 40watt outside lights on one circuit. Cable being used is 3 core NYMJ x 1.5mm. Overall length of run is approx 250 ft. Lights will be wired in "parallel" onto one switch in utility room.


Comments

  • Registered Users, Registered Users 2 Posts: 1,692 ✭✭✭Payton


    Is it ok to put 8 x 40watt outside lights on one circuit. Cable being used is 3 core NYMJ x 1.5mm. Overall length of run is approx 250 ft. Lights will be wired in "parallel" onto one switch in utility room.
    You'd be better posting this in the Electrical Forum


  • Registered Users, Registered Users 2 Posts: 22,584 ✭✭✭✭Steve


    Presume you mean in series, unless you plan on having 8 cables running back.

    8*40W = 320W = <2A. 1.5 NYMJ is loads for that.

    Bear in mind that if this is domestic, you need to be REC to legally do it. If it is commercial then you're fine.


  • Registered Users, Registered Users 2 Posts: 1,257 ✭✭✭Pete67


    Steve wrote: »
    Presume you mean in series, unless you plan on having 8 cables running back.

    8*40W = 320W = <2A. 1.5 NYMJ is loads for that.

    Bear in mind that if this is domestic, you need to be REC to legally do it. If it is commercial then you're fine.

    I think you are mixing up your series and parallel. The lights will be in parallel, live to run from a dedicated MCB to the lightswitch, switched live looped from light fitting to light fitting, neutral and earths looped similarly.

    Series wiring is very rarely used in 230V systems.


  • Registered Users, Registered Users 2 Posts: 22,584 ✭✭✭✭Steve


    Pete67 wrote: »
    I think you are mixing up your series and parallel. The lights will be in parallel, live to run from a dedicated MCB to the lightswitch, switched live looped from light fitting to light fitting, neutral and earths looped similarly.

    Apologies, you are right, I was thinking ring vs spur :D

    Yes, of course that is a parallel circuit.
    Series wiring is very rarely used in 230V systems.
    Unless it's December ;)


  • Registered Users, Registered Users 2 Posts: 89 ✭✭luimneachboy


    Cheers lads. Ya in parallel.. For a minute i thought i was losing it. My only doubt was for the run length it might overload the cable hence running 2 circuit's.