C.T.U test

  • 19-05-2016 8:11pm
    #1
    Registered Users, Registered Users 2 Posts: 5


    I've installed 8 xylux led emergency fittings on my job, they only have a permanent supply neutral and earth. There working fine during the CTU emergency test, but when I drop the breaker to do more work they don't come on. Any ideas or reasons why?


Comments

  • Registered Users, Registered Users 2 Posts: 2,567 ✭✭✭Risteard81


    Are they fed from the local lighting circuit/is the local lighting circuit being monitored?


  • Registered Users, Registered Users 2 Posts: 5 cwmoore83


    Thanks for reply, the old system is not being monitored, but in saying that the new lights have the option of been monitored . But on instructions the DA DA connections are just an option.


  • Registered Users, Registered Users 2 Posts: 2,567 ✭✭✭Risteard81


    I'm not talking about the DALI connections though - is there a bank of contactors?


  • Registered Users, Registered Users 2 Posts: 5 cwmoore83


    Yes there's 3 on the panel beside ctu