Fire damper query

  • 02-05-2016 9:41am
    #1
    Registered Users, Registered Users 2 Posts: 30


    This may seem like a stupid question but is it acceptable to install a 60 minute fire damper in a 30 minute fire wall.

    The damper carries a CE mark and has been tested in masonry & plasterboard walls, however they have only been tested for 60 minutes.

    My thinking is that the fact that the damper has been tested for over & above the rating of the fire wall it is acceptable but a colleague has told me it is not acceptable because it has not been tested for 30 mins.

    Any advise is welcome.

    Thank you in advance


Comments

  • Registered Users, Registered Users 2 Posts: 12,888 ✭✭✭✭Calahonda52


    As long as the cert for the project requires a 30 minute rating sign off then I believe you are fine to use it and your colleague is somewhat mistaken

    “I can’t pay my staff or mortgage with instagram likes”.



  • Registered Users, Registered Users 2 Posts: 3,725 ✭✭✭Metric Tensor


    I don't know the answer to this one but I can see his colleagues point:

    This piece of equipment has been proven to provide 60 minutes resistance when installed in X type of wall.

    That does not mean it will give 30 minutes in Y type of wall.

    I suppose the question is if the type of wall in which the unit is installed affects the result of its fire test. The manufacturer should be able to tell you.


  • Registered Users, Registered Users 2 Posts: 12,888 ✭✭✭✭Calahonda52


    http://www.h-v-c.com/products/pdf/S100-fire-damper-ce-mark.pdf
    is a link to a product I have seen installed.
    In the interest of trying to add to the knowledge here, my read of the CE mark is that it is given, in this case following being
    Assessed against the requirements of
    BS EN 15650

    The CE is for types of floors and walls and has detailed installation instructions for each application.
    The test is in a furnace, with the associated specified wall/floor surround.

    So IMO, if its installed as per the cert requirements for 60 minutes, then its good for 30
    HTH

    “I can’t pay my staff or mortgage with instagram likes”.