Locked fire doors

  • 24-02-2016 2:54pm
    #1
    Registered Users, Registered Users 2 Posts: 11,790 ✭✭✭✭


    Our emergency exits in work have push bars on them. They also have a security lock that operates with a key. They can be opened using the push bar from the inside when unlocked but can't be opened at all when they are locked (without the key obviously).

    They are unlocked first thing in the morning and then locked by the last person out every night.

    Are locks on emergency exits allowed or is everything ok as long as they are opened in the morning and locked at night?


Comments

  • Registered Users, Registered Users 2 Posts: 1,436 ✭✭✭AlanG


    Any pubs I worked in had doors like this and never failed a fire inspection.


  • Registered Users, Registered Users 2 Posts: 11,790 ✭✭✭✭BattleCorp


    AlanG wrote: »
    Any pubs I worked in had doors like this and never failed a fire inspection.

    We are caught between security and health and safety.

    Our security guy says that they should have locks on them as somebody could break in through the roof and then waltz out with whatever they like through the fire exit.

    Someone else says that they can't have any sort of locks on them as they might need to be used at any time (even when the building is closed).

    I can see both sides of the argument but I was wondering which one is legally correct.


  • Registered Users, Registered Users 2 Posts: 34,216 ✭✭✭✭listermint


    Having had to unlock these and lock them in years gone by in various places of student employment we never had a fire issue. These would have been large retail chains.


  • Subscribers Posts: 42,172 ✭✭✭✭sydthebeat


    1.4.3 Doors on Escape Routes
    1.4.3.1 The time taken to negotiate a closed door
    can be critical in an escape situation. Doors on
    escape routes (both within and from the building)
    should therefore be readily openable if undue delay
    is to be avoided. Accordingly the provisions in the
    paragraphs below should be met.

    1.4.3.2 Door fastenings - In general, doors on
    escape routes, whether or not the doors are fire
    doors, should either not be fitted with lock, latch or
    bolt fastenings, or they should only be fitted with
    simple fastenings that can be readily operated in the
    direction of escape without the use of a key.


    Where security on final exit doors is an important
    consideration, such as some assembly or commercial
    uses, panic bolts should be used to secure doors.

    Where additional security is required when the
    premises is not in use, hardware which is fully
    removable should be used
    . The following
    recommendations apply to buildings, or parts of
    buildings which are used for assembly or recreation
    (Purpose Group 5):-
    (a) Exit doors from areas holding more than 50
    people should either be free from fastenings or
    be fitted with panic bolts complying with I.S. EN
    1125 1997.
    (b) Doors, other than those covered by item (a),
    should be fitted only with simple fastenings that
    can be operated from the escape side of the
    door without the use of a key.
    Attention is drawn to the provisions of the Fire
    Safety in Places of Assembly (Ease of Escape),
    Regulations, 1985 (S.I. No. 249 of 1985).
    Information about door closing and hold open
    devices for fire doors is given in Appendix B.


    so in general key locks should NOT be used... unless previous agreed with Fire Officers. It comes down to fire management as well ie who opens and closes, who has keys, are they stored on site etc etc


  • Moderators, Society & Culture Moderators Posts: 40,366 Mod ✭✭✭✭Gumbo


    I see this every day. Pubs and nightclubs would have similar arrangements. Aslong as they are open while the building is in use then the fire officer shouldn't have a problem. But, if you want to satisfy your curiosity and out your mind at ease you can send an email to buildingcontrol@dublincity.ie and they can enquire about it or pass it onto fire prevention who may or may not inspect the premises.


  • Advertisement
  • Registered Users, Registered Users 2 Posts: 3,057 ✭✭✭civdef


    This tends to work fine for main doors, where people will be going in / coming out often enough to make sure it's done. On rarely used escape doors though it's a recipe for failure and generally isn't allowed, unless a very robust management system is in place.

    If it's a post 1992 building, the fire cert could be worth checking - the approved compliance report generally just says something along the lines of "will comply with Paragraph 1.4.3.2", i.e. easily openable from the inside without the use of a key. If you wanted to have security locks on fire doors in conjunction with a management systems, this would need to have been specifically stated at FSC stage.