Replacing Grasslin Ecosave Timer with Heatmiser-hw

  • 23-11-2015 6:03pm
    #1
    Registered Users, Registered Users 2 Posts: 2,857 ✭✭✭


    I currently have a Grasslin Ecosave timer as per the attached photo.
    The hot water tank is electric.

    Is it possible to replace this with a heatmiser-hw or similar thermostat?


Comments

  • Registered Users, Registered Users 2 Posts: 8,565 ✭✭✭K.Flyer


    Heatmiser is primarily designed for central heating systems being linked into peripherals with low amp ratings of approx 3 - 5 amps.
    Immersion elements have a much higher rating of approx 12 - 13 amp, probably not a good idea to mix the two.