Oil burner won't fire up

  • 19-11-2015 5:53pm
    #1
    Registered Users, Registered Users 2 Posts: 98 ✭✭


    Hi guys i have an oil burner and yesterday it just stopped working so we thought it was the oil and we got oil today and we were just going to bleed it but there was oil coming out

    so then we wanted to start up the burner and we can hear it running but it doesn't fire up as we can here the spark like every few seconds trying to fire up but it actually won't fire up.

    So if anyone know's what could be wrong please let me know.

    Burner Model Number: Grant 50-90 Euroflame


Comments

  • Registered Users, Registered Users 2 Posts: 1,560 ✭✭✭Prenderb


    Sounds similar to a problem I had a couple of years ago, we needed a new pump. If that's what it is, we paid around 90 for a grundfos, + fitting costs.


  • Registered Users, Registered Users 2 Posts: 98 ✭✭tomstud12


    Prenderb wrote: »
    Sounds similar to a problem I had a couple of years ago, we needed a new pump. If that's what it is, we paid around 90 for a grundfos, + fitting costs.

    But since the oil is going into the burner would it not be something else?


  • Registered Users, Registered Users 2 Posts: 152 ✭✭Walter Becket


    The solonid coil is a common part to go on that model burner you can check it with a multi meter or put something name if iron in the hole when it should be powered and see if you can feel the magnetic field.


  • Moderators, Home & Garden Moderators Posts: 6,470 Mod ✭✭✭✭Wearb


    tomstud12 wrote: »
    Hi guys i have an oil burner and yesterday it just stopped working so we thought it was the oil and we got oil today and we were just going to bleed it but there was oil coming out

    so then we wanted to start up the burner and we can hear it running but it doesn't fire up as we can here the spark like every few seconds trying to fire up but it actually won't fire up.

    So if anyone know's what could be wrong please let me know.

    Burner Model Number: Grant 50-90 Euroflame

    When you say "there was oil coming out" are you talking of the bleed point in the pump?

    It takes an experienced ear to hear the spark. I think what you are hearing is an attempt to fire.
    How many inches if oil do you have in the tank ? When was it last serviced ?


  • Registered Users, Registered Users 2 Posts: 3,991 ✭✭✭jimf


    not too sure what you are hearing it could possibly be overaired


  • Advertisement
  • Registered Users, Registered Users 2 Posts: 98 ✭✭tomstud12


    Wearb wrote: »
    When you say "there was oil coming out" are you talking of the bleed point in the pump?

    It takes an experienced ear to hear the spark. I think what you are hearing is an attempt to fire.
    How many inches if oil do you have in the tank ? When was it last serviced ?

    yes i mean attempt to fire
    and we got 500 litres just today
    and it was serviced not even a year ago


  • Closed Accounts Posts: 1,590 ✭✭✭agusta


    Are you saying it keep attempts to fire but does not go to lock out?


  • Registered Users, Registered Users 2 Posts: 98 ✭✭tomstud12


    agusta wrote: »
    Are you saying it keep attempts to fire but does not go to lock out?

    Yes it attempts to fire and what do you mean by lock out? like if i leave it on it just keeps trying to fire up every few seconds but i can hear the fan or what ever makes the other noise.


  • Closed Accounts Posts: 1,590 ✭✭✭agusta


    My opinion.the burner lights for a split second and the fan/ air is blowing out the flame.if nobody adjusted the air settings it points to not enough fuel getting through the nozzle.it could be just a partially blocked nozzle or the fuel pump.you will need a pressure gauge to test the pump.what model and make of burner is it..,you can do a simple test by giving the burner less air to see will it start,my money would be on a partially blocked nozzle


  • Moderators, Home & Garden Moderators Posts: 6,470 Mod ✭✭✭✭Wearb


    tomstud12 wrote: »
    yes i mean attempt to fire
    and we got 500 litres just today
    and it was serviced not even a year ago

    Sounds like pump or nozzle problem. It may take a pressure gauge to diagnose if it's a pump problem.

    Do you have the last service report. I am interested in knowing what O2 was then. JimF is considering that that may be the problem


  • Advertisement
  • Moderators, Home & Garden Moderators Posts: 6,470 Mod ✭✭✭✭Wearb


    :( Sorry for parroting Agusta. Was typing while you were posting.


  • Closed Accounts Posts: 1,590 ✭✭✭agusta


    Wearb wrote: »
    :( Sorry for parroting Agusta. Was typing while you were posting.
    its good that we can both came up with the same answer to diagnose the fault


  • Registered Users, Registered Users 2 Posts: 98 ✭✭tomstud12


    agusta wrote: »
    My opinion.the burner lights for a split second and the fan/ air is blowing out the flame.if nobody adjusted the air settings it points to not enough fuel getting through the nozzle.it could be just a partially blocked nozzle or the fuel pump.you will need a pressure gauge to test the pump.what model and make of burner is it..,you can do a simple test by giving the burner less air to see will it start,my money would be on a partially blocked nozzle
    Wearb wrote: »
    Sounds like pump or nozzle problem. It may take a pressure gauge to diagnose if it's a pump problem.

    Do you have the last service report. I am interested in knowing what O2 was then. JimF is considering that that may be the problem

    You see it stopped working yesterday and so i thought it was the oil cause we didn't order for a long time so then i ordered oil yesterday for today but then when i came home my wife said she checked the tank when the dude with the oil came and said that the tank was half full so we didn't run out of oil so something must of went off as we didn't touch the boiler.


  • Moderators, Home & Garden Moderators Posts: 6,470 Mod ✭✭✭✭Wearb


    It may have always been getting too much air, but only reacting to it now that it has gotten colder and the air denser. That is why I asked for O2


  • Registered Users, Registered Users 2 Posts: 98 ✭✭tomstud12


    Wearb wrote: »
    It may have always been getting too much air, but only reacting to it now that it has gotten colder and the air denser. That is why I asked for O2

    What is the O2?


  • Registered Users, Registered Users 2 Posts: 3,991 ✭✭✭jimf


    pump could be slipping also if burner is a r40 it will be obvious by the damper opening and closing constantly

    only another uneducated guess for ye parrots wear/agusta


  • Registered Users, Registered Users 2 Posts: 98 ✭✭tomstud12


    and the
    Burner Model Number: Grant 50-90 Euroflame


  • Moderators, Home & Garden Moderators Posts: 6,470 Mod ✭✭✭✭Wearb


    tomstud12 wrote: »
    What is the O2?

    Oxygen. It will be on service report or attached printout.


  • Registered Users, Registered Users 2 Posts: 152 ✭✭Walter Becket


    Have you cleaned the photocell it's easy to do .


  • Closed Accounts Posts: 1,590 ✭✭✭agusta


    tomstud12 wrote: »
    and the
    Burner Model Number: Grant 50-90 Euroflame

    That is the make of boiler..,the burner would be a riello,what model


  • Advertisement
  • Registered Users, Registered Users 2 Posts: 98 ✭✭tomstud12


    agusta wrote: »
    That is the make of boiler..,the burner would be a riello,what model

    Oh okay sorry am will check


  • Registered Users, Registered Users 2 Posts: 98 ✭✭tomstud12


    Wearb wrote: »
    Oxygen. It will be on service report or attached printout.

    Okay i will try to look for that and will let you know


  • Registered Users, Registered Users 2 Posts: 98 ✭✭tomstud12


    Have you cleaned the photocell it's easy to do .

    Where can i find that?


  • Registered Users, Registered Users 2 Posts: 152 ✭✭Walter Becket


    Have you cleaned the photocell it's easy to do.


  • Registered Users, Registered Users 2 Posts: 98 ✭✭tomstud12


    Okay are there any steps i should take to check what could be the problem?


  • Registered Users, Registered Users 2 Posts: 152 ✭✭Walter Becket


    tomstud12 wrote: »
    Have you cleaned the photocell it's easy to do .

    Where can i find that?
    Add your reply here.
    If it's the burner I think it is on the front there's a black Plastic cover held on by an allen head screw take off this and under it you'll see a wire going into what looks like a plastic connector pull this out and clean the glass bit on the end.


  • Closed Accounts Posts: 1,590 ✭✭✭agusta


    tomstud12 wrote: »
    Okay are there any steps i should take to check what could be the problem?

    model of burner or a picture..


  • Registered Users, Registered Users 2 Posts: 152 ✭✭Walter Becket


    agusta wrote: »
    tomstud12 wrote: »
    Okay are there any steps i should take to check what could be the problem?

    model of burner or a picture..

    We really need this info.


  • Moderators, Home & Garden Moderators Posts: 6,470 Mod ✭✭✭✭Wearb


    I think we have gone as far as we can in helping. Most of the conclusions we have come to will require a techintion to fix.


  • Advertisement
  • Registered Users, Registered Users 2 Posts: 98 ✭✭tomstud12


    here's a few pictures


  • Registered Users, Registered Users 2 Posts: 98 ✭✭tomstud12


    Wearb wrote: »
    I think we have gone as far as we can in helping. Most of the conclusions we have come to will require a techintion to fix.

    Yeah i guess i will have to call the technician at last.


  • Registered Users, Registered Users 2 Posts: 152 ✭✭Walter Becket


    To clean photocell remove the red cover pull out the photocell and clean the end with a damp cloth. It's the thing with a wire going into it right in the middle of the burner at the top


  • Registered Users, Registered Users 2 Posts: 98 ✭✭tomstud12


    To clean photocell remove the red cover pull out the photocell and clean the end with a damp cloth. It's the thing with a wire going into it right in the middle of the burner at the top

    And what color is the wire going into it?


  • Registered Users, Registered Users 2 Posts: 3,991 ✭✭✭jimf


    black


  • Registered Users, Registered Users 2 Posts: 98 ✭✭tomstud12


    jimf wrote: »
    black

    Okay thanks and do i just pull it out and clean it or are there any screws?


  • Advertisement
  • Registered Users, Registered Users 2 Posts: 3,991 ✭✭✭jimf


    no screws just wiggle it gently from side to side don't just try and pull it straight back

    you should see a little clear glass eye at the end a moist cotton bud is handy for cleaning it don't tell agusta


  • Registered Users, Registered Users 2 Posts: 3,991 ✭✭✭jimf


    on another note that flue on top of boiler looks like its leaking pocs as well and does look smoky

    maybe time for a service and tune up is long overdue


  • Closed Accounts Posts: 198 ✭✭Nap702


    tomstud12 wrote: »
    jimf wrote: »
    black

    Okay thanks and do i just pull it out and clean it or are there any screws?

    How did you fix this