Advertisement
If you have a new account but are having problems posting or verifying your account, please email us on hello@boards.ie for help. Thanks :)
Hello all! Please ensure that you are posting a new thread or question in the appropriate forum. The Feedback forum is overwhelmed with questions that are having to be moved elsewhere. If you need help to verify your account contact hello@boards.ie

Mains pressure rising when boiler is on .

  • 05-11-2015 10:22PM
    #1
    Registered Users, Registered Users 2 Posts: 957 ✭✭✭


    Can anyone shed some light .
    We have a pressurised system and oil boiler . When the boiler is off we have in and around 2.5 bar . This is the reading on the up gauge from the mains . When
    The oil Boiler is turned on (water and heating) the gauge pressure from the mains rises to 5 bar .
    What could be causing this .

    The water tank pump is bypassed. Sotheby's gauge should be reading mains pressure.


Comments

  • Registered Users, Registered Users 2 Posts: 369 ✭✭Kealyboy


    Can anyone shed some light .
    We have a pressurised system and oil boiler . When the boiler is off we have in and around 2.5 bar . This is the reading on the up gauge from the mains . When
    The oil Boiler is turned on (water and heating) the gauge pressure from the mains rises to 5 bar .
    What could be causing this .

    The water tank pump is bypassed. Sotheby's gauge should be reading mains pressure.
    I presume you mean boiler/system pressure. For starters the system pressure should be 1 bar when boiler is off (system cold). If the pressure rises when heating is on this indicates that the mostly likely cause is your pressure vessel is shot.

    Filling loop should be disconnected when system is topped up to required pressure also


  • Moderators, Home & Garden Moderators Posts: 6,492 Mod ✭✭✭✭Wearb


    Why the hell is it rising to 5 bar. You have a very dangerous setup. The system should be protected by a 3 bar pressure relief valve. I would not use it until sorted.


  • Registered Users, Registered Users 2 Posts: 957 ✭✭✭homewardbound11


    Thanks for the help.

    Better get the plumber in so .
    The gauge I see is the one at the mains after the water pump ( in the garage)

    So in the garage it is mains to 500l tank with pump to gauge .
    There are other things in the loop but I just wouldn't know . Think they are bypass option and auto fill. Also some connections on the oil boiler there too.

    The only reason I got alerted was the outside tap was leaking . It was connected to the mains just before the gauge .

    As soon as I get the plumber in ill post back .


  • Moderators, Home & Garden Moderators Posts: 6,492 Mod ✭✭✭✭Wearb


    Good. Make sure to ask your plumber (1)why your heating boiler is driving that gauge up. (2) why your boiler pressure relief valve isn't letting water by at above 3 bar.


Advertisement