Vokera repair galway city?

  • 25-09-2015 5:24pm
    #1
    Registered Users, Registered Users 2 Posts: 1,475 ✭✭✭


    Came home this afternoon and not a mag out of the boiler.

    Could anyone suggest someone who could repair

    It is 10 years old and had the fan replaced last year.

    Thanks


Comments

  • Registered Users, Registered Users 2 Posts: 12,870 ✭✭✭✭Dtp1979


    Came home this afternoon and not a mag out of the boiler.

    Could anyone suggest someone who could repair

    It is 10 years old and had the fan replaced last year.

    Thanks

    Is your room thermostat turned up high enough?


  • Registered Users, Registered Users 2 Posts: 1,475 ✭✭✭phelixoflaherty


    Ya.
    Tried it for hot water too
    Tried sitting room fire too so there is a gas supply.
    The motorised valves are working too ( dunno where they draw their power from)


  • Registered Users, Registered Users 2 Posts: 12,870 ✭✭✭✭Dtp1979


    Ya.
    Tried it for hot water too
    Tried sitting room fire too so there is a gas supply.
    The motorised valves are working too ( dunno where they draw their power from)

    What's the pressure gauge reading on the boiler?


  • Registered Users, Registered Users 2 Posts: 1,475 ✭✭✭phelixoflaherty


    Zero. But it was always like that. The pressure would increase with temp


  • Registered Users, Registered Users 2 Posts: 1,475 ✭✭✭phelixoflaherty


    Just pressurised the valve thingy up to 1 bar and no joy even after allowing system time to "boot up"


  • Advertisement
  • Registered Users, Registered Users 2 Posts: 12,870 ✭✭✭✭Dtp1979


    Just pressurised the valve thingy up to 1 bar and no joy even after allowing system time to "boot up"

    Is there any lights flashing on the boiler? Any red lights?


  • Registered Users, Registered Users 2 Posts: 1,475 ✭✭✭phelixoflaherty


    Got a local lad on recommendation.

    Said it was a fuse on the PCB.

    Come to think we had a fault here during the week which triped some of the breakers.

    Up and running again thanks for replys


  • Registered Users, Registered Users 2 Posts: 1,475 ✭✭✭phelixoflaherty


    In the end it was the PCB
    Replaced for 210 euro.